[RE-wrenches] Dark Starting Simpliphi PHI3.5 batteries
Howie Michaelson
Howie.Michaelson at gmail.com
Wed Jul 27 19:46:17 PDT 2022
Thanks Wallace. I will return to the site and check the voltage again, but
I believe when I read it it was in the teens. However, I did run into the
in rush and shut down issue you mentioned the first time I tried
restarting, but when I tried it again, the batteries didn't put anything
out. I will talk with simpliphi and see if we can get things going.
Howie
On Wed, Jul 27, 2022, 10:38 PM Wallace Stahle via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hold off on that 48 volt charger Howie,
>
> I was called a while back with the same issue on a set of five of the same
> model battery. All shut off internally. Had the same inverter and CC too.
> I called Simpliphi which I recommend you do also and was told to turn off
> all inputs and outputs to battery, close the breaker on each unit
> individually and read the open circuit voltage. If 24 v or above simply
> close the 3 breakers before engaging the inverter breaker as the capacitor
> inrush can fool the BMS of the battery and shut it off which I found out
> when I first shop charged the new batteries individually. If battery shuts
> down upon inverter connection then toggling the battery breaker again the
> inverter will connect and you charge with generator as the inverter can now
> function with the small amount of reserve power present. And/or the solar
> as conditions dictate.
>
> In my case one of the batteries was 23.7 V but still accepted a charge and
> have apparently functioned well for the customer. Job was installed by
> others.
>
> I hope that helps.
> Wallace Stahle
> Future Electric Energy Co
> PO Box 236
> Willits, CA 95490
> 707-459-0474
> Lic.#C10-762093
> future at pacific.net
>
> On Jul 27, 2022, at 6:58 PM, Howie Michaelson via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Hi All,
> I was called into a job of a previously off-grid system that new owners
> had an electrician bring the grid to, but the batteries ( a pair of
> Simpliphi 3.5, which I have no experience with) have been dead for an
> unknown period of time previously. I am trying to figure out the easiest
> way to restart the system which has a VFX 3648 and FM60. I'm thinking the
> easiest way is to bring in a 48volt charger to get the battery voltage up
> high enough to start the FM60 and/or VFX, but that means purchasing a 48
> volt charger, since I don't have any Iotas sitting around any more. If
> anyone has an easier way to restart the batteries I'd love to hear it.
> Thanks,
> Howie
>
> *Howie Michaelson**Sun Catcher*
>
> *NABCEP Certified Solar PV Installer™*
>
> *Solar Electric Systems Sales & Service802-272-0004*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20220727/ba1c0524/attachment.htm>
More information about the RE-wrenches
mailing list