[RE-wrenches] Question

penobscotsolar at midmaine.com penobscotsolar at midmaine.com
Thu Jun 15 16:09:52 PDT 2017


I re-read and see that I need to clarify my earlier question. The 400 amp,
120/208 panel has a main breaker that will be used for the utility input,
coming in on 3/0 copper.  The four 60 amp breakers will be used because
the four 10 kW inverters maximum ac output is 48 amps each (x 1.25 =60
amps ocpd). On the opposite end of the 400 amp panel there are main lugs
which will be used to feed the generator transfer switch, essentially,
because the inspector says we cannot put more than "two in, one out" on
the gentran. These wires to the gentran are what I am wondering how best
to size. Common sense tells me they should be rated the same as the main
panel breaker from the utility. Is this a correct assumption?


> Esteemed wrenches,
>    We're working often in the Bahamas and now that net metering is
> approved there, the inspectors are far behind in their comprehension.
> That said, we are currently required to combine the utility with the PV
> in a main load center before going to the generator transfer switch. I
> have a 400 amp rated load center with a 200 amp, 120/208 main breaker
> on it, as well as four 60 a, 3 pole breakers that will be fed from four
> 10 kw inverters. My question is, will it be necessary to use wire rated
> at 400 amps or can I use wire rated for the main breaker? Thank you for
> your input. It might be a stupid question, but I am stymied here....it
> might just be the Lyme, not sure.....oh, and it's CEC 2015 down there,
> but I suspect it will align with NEC 2014.
>
> Thanks again,
> Daryl DeJoy
> NABCEP Certified PV
> Penobscot Solar Design
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>





More information about the RE-wrenches mailing list