[RE-wrenches] Xantrex XW 6048A unregulated during charging
Jason Lerner
wapalco at rockisland.com
Thu May 4 09:01:09 PDT 2017
This system was 9 years old and I was called in to put in a new battery bank. We added a Combox, but did not update the firmware on the XW’s since there had only been one update, it did not add any functionality that the customer needed, and I didn’t want to introduce any new problems (exactly like you and others have mentioned) with a new firmware update.
The Combox had the most recent Firmware, is there a possibility it doesn’t play nice with the older firmware of the inverters??
Thanks very much,
Jason
> On May 4, 2017, at 7:03 AM, Dave Angelini Offgrid Solar <offgridsolar at sti.net> wrote:
>
> I would add that after loading firmware on Outback or Schneider there
> sometimes have been cases where it showed the new firmware but it was
> still running the old.
> The solution was to choose original factory default firmware. After that
> the unit would load the latest firmware that you had previously installed.
> Now that is maddening. There are so many XW's and Outbacks out there that
> I am surprised at how well they run. I am not a big fan of loading new
> firmware unless you have to.Most of this gear is fine with what it had
> offgrid. Leave it alone unless you know exactly why you are changing. The
> firmware has release notes and you should read them. The combox has recent
> firmware that stopped the "bricking " issue it had. I would do that one
> for sure! I like the config tool also along with combox.
>
>
>> As with anything these days I would make damn sure that the firmware OF
>> ALL components in the system have been updated w/ the latest firmware
>> prior to changing anything. I personally am not a big fan of the com box
>> and I have the âCon figâ tool and I find after the learning curve its
>> the best method of addressing info & updating. Mis matched firmware seems
>> to be the # 1 issue w/ all the manufactures today. Tump
>>> On May 3, 2017, at 6:17 PM, Jason Lerner <wapalco at rockisland.com> wrote:
>>>
>>> Hello All,
>>>
>>> Iâm working on a system with 3 Xantrex XW 6048âs that has grid on
>>> AC1 and a 20 kw generator on AC2. When charging from grid it regulates
>>> during an absorption charge at 58.2 where it should. When charging from
>>> AC 2 - generator, the battery Voltage rises above 62 VDC, but not every
>>> single time. All the settings are correct, EQ is turned off, and if it
>>> accidentally got turned on is set at the same Voltage as the absorption
>>> setting. Customer has a brand new 33 kWh AGM battery bank, that I
>>> would rather not fry. This is a battery backup system with no PV.
>>>
>>> I have checked all the temperature sensors (they seem good) and tried
>>> charging with them plugged in, and with them unplugged and it doesnât
>>> seem to change the situation.
>>>
>>> Has anybody else seen this happen before? Any suggestions?
>>>
>>> Thanks very much,
>>>
>>> Jason Lerner
>>> Waldron Power and Light Co.
>>> (888) 927-2526
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>> Tump at swnl.net
>>> <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>
>>> www.SWNL.net
>>> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>>> Solarwinds Northernlights
>>> Serving Mid Coast Maine & Northern California
>>> 207-832-7574 Cl. 610-517-8401
>>> Blair "TUMP" May
>>> ******** MAINE'S CHARTER ********
>>> NABCEP "Certified PV Installer"
>>>
>>> ******** MAINE'S CHARTER ********
>>> Trace Xantrex "Certified" Dealer / Installer"
>>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list