[RE-wrenches] Xantrex XW 6048A unregulated during charging

Tump tump at swnl.net
Thu May 4 04:39:07 PDT 2017


As with anything these days I would make damn sure that the firmware OF ALL components in the system have been updated w/ the latest firmware prior to changing anything. I personally am not a big fan of the com box and I have the “Con fig” tool and I find after the learning curve its the best method of addressing info & updating. Mis matched firmware seems to be the # 1 issue w/ all the manufactures today. Tump
> On May 3, 2017, at 6:17 PM, Jason Lerner <wapalco at rockisland.com> wrote:
> 
> Hello All,
> 
> I’m working on a system with 3 Xantrex XW 6048’s that has grid on AC1 and a 20 kw generator on AC2.  When charging from grid it regulates during an absorption charge at 58.2 where it should.  When charging from AC 2 - generator, the battery Voltage rises above 62 VDC,  but not every single time.  All the settings are correct, EQ is turned off, and if it accidentally got turned on is set at the same Voltage as the absorption setting.  Customer has a brand new 33 kWh AGM battery bank,  that I would rather not fry.  This is a battery backup system with no PV.
> 
> I have checked all the temperature sensors (they seem good) and tried charging with them plugged in,  and with them unplugged and it doesn’t seem to change the situation. 
> 
> Has anybody else seen this happen before?  Any suggestions?
> 
> Thanks very much,
> 
> Jason Lerner
> Waldron Power and Light Co.
> (888) 927-2526
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>               www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                              
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170504/506390e0/attachment-0002.html>


More information about the RE-wrenches mailing list