[RE-wrenches] Failed L16 with perfect Sp.Gr.
Ray
ray at solarray.com
Thu Apr 27 10:51:19 PDT 2017
That was my point: voltage is not very helpful on the 2 v L16s, as all 3
cells are internally paralleled. With the Flir I was able to see all
the dead cells in the set in seconds.
R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760
On 4/27/17 10:22 AM, Dave Angelini Offgrid Solar wrote:
> The FLIR is nice but SG and voltage would have told the same thing, would
> it not?
> I have excellent experience with the L16 2V cells but will be switching to
> the LG RESU 10 very soon for my clients.
>
>> Here's a thermal image from a recent inspection of 2 v Trojan L16REs.
>> Notice the normal batteries above and below, they are cool blue, running
>> around 75F
>>
>> 2 of the cells of the center battery are obviously shorted. Cell
>> voltage was 2.07 v compared to about 2.3 to 2.4 v for surrounding good
>> batteries. Dead cells are much easier to find on 6 v batteries. I
>> wouldn't have found this without the Flir 167.
>>
>> About 1/4 of the batteries in this set had hot cells; 25 -30 deg F
>> warmer. Obviously time for some fresh lead. Owner couldn't recall how
>> old the set was, he thought 2 to 4 years. Rated at 1000 cycles to 80%
>> DOD, these Trojan RE batteries should do much better than that. I have
>> never been impressed with L16s anyway. John, my experience has also
>> been: higher Capacity = more premature cell failures.
>>
>> R. Ray Walters
>> Chief Technical Officer, RemoteSolar.com
>> BS Mech Engineering, 1988
>> Former NABCEP Certified, 2004-2016
>> Licensed Master ELectrician, Colorado
>> 303 505-8760
>>
>> On 4/26/17 2:09 PM, John Blittersdorf wrote:
>>> Wallace,
>>> I installed some Interstate RE batteries (green case) L16's that
>>> supposedly are made by US Battery. As with Trojan and other High
>>> Capacity L16's I had several cell failures. I have always felt that
>>> gleaning more amp hours from the same box must lead to cutting corners
>>> on robustness. I have found that often when the batteries are full,
>>> they work OK for awhile but as the voltage drops and the current flow
>>> rises, the cell will eventually drop out. Other adjacent batteries in
>>> the string often overcharge to compensate. In my case with the green
>>> batteries, they were about 2 years old as well. I took them back to
>>> my distributor and replaced them with standard L16's at a special pro
>>> rated price. I have found that all lead acid batteries that have
>>> problems seem to first have a cell failure somewhere along the line
>>> and finally the capacity diminishes to the point that it is an
>>> annoyance. Seems bad cells seem more numerous lately.
>>>
>>> John Blittersdorf
>>> Rob Stubbins Solar
>>>
>>>
>>> On Wed, Apr 26, 2017 at 11:54 AM, Wallace Stahle <wstahle at pacific.net
>>> <mailto:wstahle at pacific.net>> wrote:
>>>
>>> Hi Folks,
>>>
>>> I was called by a customer with the complaint of the MS4024
>>> inverter shut down and ME-ARC controller and Trimetric acting
>>> strange, intermittent and even even showing 29 volts at times.
>>>
>>> The batteries are four 2.5 year old US battery L16XC 380 AH and
>>> checking each battery showed one at 4.8 v under charge while the
>>> other three were at 7+ volts and no current.
>>>
>>> Meanwhile the specific gravity was high on all cells and even a
>>> week after removal are up at 1.275 on all three cells.
>>>
>>> I suspect an open in the cell interconnects with enough continuity
>>> to read volts but not conduct current.
>>>
>>> My question is what have any of you seen n this regard and any
>>> knowledge of cause of such a failure.
>>>
>>> Your insights and experience are greatly appreciated.
>>>
>>> They were installed by others and are out of warranty. I donated a
>>> serviceable used USB L16 to get her back to a working system.
>>> She did recall her Ex stating along the lines of "oh this one has
>>> a problem but dont worry, it'll come around" as they were installed.
>>>
>>> Many thanks,
>>>
>>> Wallace Stahle
>>> Future Electric Energy Co
>>> P O Box 236
>>> Willits, CA 95490
>>> future at pacific.net <mailto:future at pacific.net>
>>> CA Lic.# C10-762093
>>> 707-459-0474 <tel:707-459-0474>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <http://www.re-wrenches.org/etiquette.htm>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list