[RE-wrenches] 690.47(D)

Jason Szumlanski jason at floridasolardesigngroup.com
Mon Jan 30 11:54:49 PST 2017


I don’t think that was the intention necessarily, but I have argued the
same thing with varying degrees of success. Fortunately (?) we are still on
2011 here, but 2014 is coming and hopefully AHJs will remain permissive of
no additional electrode if the home already has one within 6 feet of the
service entrance (which it almost always does).

Jason Szumlanski



On Mon, Jan 30, 2017 at 1:57 PM, William Miller <william at millersolar.com>
wrote:

> Mark:
>
> For micro-inverter systems I have successfully argued the application of
> Exception No. 1. in that the load is the micro-inverter.
>
> William
>
>
> Lic 773985
> millersolar.com
> 805-438-5600
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of markf at berkeleysolar.com
> Sent: Monday, January 30, 2017 10:24 AM
> To: re-wrenches at lists.re-wrenches.org
> Subject: [RE-wrenches] 690.47(D)
>
> Folks,
>
> NEC 2014 is in effect in California. I just pulled a permit for a
> residential system and it had a little stamp that had 690.47(D) circled as
> a requirement.
>
> Anyone worked with AHJ's in California who are now requiring this? I am
> planning to not install the electrode, siting Exception 2 and trying to
> say that the existing electrode next to the build is "next to the array"?
>
> Mark
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
> l
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170130/a2fec8e8/attachment-0002.html>


More information about the RE-wrenches mailing list