[RE-wrenches] 690.47(D)

William Miller william at millersolar.com
Mon Jan 30 10:57:35 PST 2017


Mark:

For micro-inverter systems I have successfully argued the application of
Exception No. 1. in that the load is the micro-inverter.

William


Lic 773985
millersolar.com
805-438-5600

-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of markf at berkeleysolar.com
Sent: Monday, January 30, 2017 10:24 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] 690.47(D)

Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark