[RE-wrenches] Hidden corrosion caused catastrophic battery system failure
cwarfel
cwarfel at entech-engineering.com
Sat Jan 21 06:54:10 PST 2017
Hi David, do you have any pictures of this that could be shared? Chris
On 1/20/2017 12:52 PM, Dave Palumbo wrote:
>
> Following is an entry from a Backwoods Solar email that I received
> today. I would like to share this as a teachable point for RE techs
> not familiar enough with proper battery bank care and as a reminder
> for those of us with years of storage battery experience.
>
> I have underlined the two issues in the Backwoods email copied below
> my bullet points to highlight the teachable issues.
>
> ·Checking wiring connections: Check not only for tightness but also
> for temperature. There are two simple methods that work well: #1) Use
> an IR Thermometer to ensure all connections are of a similar moderate
> temperature. #2) Use your fingers to check temperatures. I'm
> practiced at this second method because inexpensive IR thermometers
> were not available when I began to care for storage batteries. I
> simply use my bare fingers (with a light coating of petroleum jelly)
> to wiggle test each battery cable at the battery terminal. Fingers are
> sensitive enough to gauge proper temperature. I have easily found
> several warm or hot connection points over the years caused by loose
> or corroded hardware. Do this as preventive maintenance every time you
> water the batteries or bi-monthly with sealed cells. Corrective
> measures (tightening, or taking apart and cleaning, or replacing, and
> reinstalling) are taken immediately when a warmer than usual
> connection is identified.
>
> ·It is not recommended by most veteran wrenches to use any
> "anti-corrosion paste" on the terminal connections. This has been
> discussed a few times over the years on the Wrenches list. Most of us
> have found that a thin coating of petroleum jelly (Vaseline is one
> brand) does the best job of protecting against corrosion while still
> allowing some visual inspection.
>
> from Backwoods Solar 1/20/17. << This past summer Backwoods had a
> visit from one of our retired co-workers, xxxxx. While it is always
> good to have friends visit, the circumstances for his dropping by were
> less than ideal.
>
> A small, catastrophic failure had led to the loss of a battery bank,
> two inverters, and a voltage converter. Ultimately, the failure was
> traced back to a single nut and bolt in the battery bank cable
> connections, that had developed hidden corrosion over time. Corrosion
> causes resistance to the flow of electricity, which in turn generates
> heat. With enough corrosion, and enough current flow, the amount of
> heat generated can be sufficient to melt battery terminal connections;
> which is exactly what happened in xxxxx’s case. The melted metal
> flowed between the negative and positive terminals of his industrial
> battery, causing a high power short that was beyond the capabilities
> of any of the circuit protection, resulting in the damage to the
> equipment.
>
> Now keep in mind, xxxxx is one of the more detail-oriented people
> we’ve had here at Backwoods. The discipline of a military background,
> along with critical thinking of an engineer, were still not enough to
> overlook one very tiny detail. xxxxx does his mechanical maintenance
> on a routine schedule; _checking for tightness in wiring connections_,
> cleaning accumulated spray off battery tops, cleaning out dust and
> spider webs, _and keeping his battery terminal posts coated with
> anti-corrosion paste._ This is not the type of person you’d expect to
> see such a failure.
>
> So what happened? It all boiled down to the battery terminal
> connections. What xxxxx had NOT done, was dissembled the nut and
> bolts from the battery terminals and cables to check for internal,
> hidden corrosion. It had been about 6 years since he had done that
> level of inspection. When previously reviewed, the hardware had been
> thoroughly inspected, cleaned, and re-assembled, and then coated with
> _anti-corrosion paste on the exterior_. In one of the 16 nut/bolt
> pairs, a small bit of contamination or moisture must have been left
> trapped inside. Over the course of the next six years, the corrosion
> grew, contaminating the entire connection; but was NOT visible
> externally at all! >>
>
> Best regards,
>
> Dave
>
> David Palumbo
>
> Independent Power LLC
>
> 462 Solar Way Drive
>
> Hyde Park, VT 05655
>
> 802-371-8678 cell
>
> 802-888-4917 home
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170121/ce418a8c/attachment-0002.html>
More information about the RE-wrenches
mailing list