[RE-wrenches] Hidden corrosion caused catastrophic battery system failure

Dave Palumbo palumbo131m at gmail.com
Fri Jan 20 09:52:50 PST 2017


Following is an entry from a Backwoods Solar email that I received today. I
would like to share this as a teachable point for RE techs not familiar
enough with proper battery bank care and as a reminder for those of us with
years of storage battery experience. 

I have underlined the two issues in the Backwoods email copied below my
bullet points to highlight the teachable issues.

.         Checking wiring connections: Check not only for tightness but also
for temperature. There are two simple methods that work well: #1) Use an IR
Thermometer to ensure all connections are of a similar moderate temperature.
#2)  Use your fingers to check temperatures. I'm practiced at this second
method because inexpensive IR thermometers were not available when I began
to care for storage batteries. I simply use my bare fingers (with a light
coating of petroleum jelly) to wiggle test each battery cable at the battery
terminal. Fingers are sensitive enough to gauge proper temperature. I have
easily found several warm or hot connection points over the years caused by
loose or corroded hardware. Do this as preventive maintenance every time you
water the batteries or bi-monthly with sealed cells. Corrective measures
(tightening, or taking apart and cleaning, or replacing, and reinstalling)
are taken immediately when a warmer than usual connection is identified.

.         It is not recommended by most veteran wrenches to use any
"anti-corrosion paste" on the terminal connections. This has been discussed
a few times over the years on the Wrenches list. Most of us have found that
a thin coating of petroleum jelly (Vaseline is one brand) does the best job
of protecting against corrosion while still allowing some visual inspection.

from Backwoods Solar 1/20/17.  << This past summer Backwoods had a visit
from one of our retired co-workers, xxxxx.  While it is always good to have
friends visit, the circumstances for his dropping by were less than ideal.

A small, catastrophic failure had led to the loss of a battery bank, two
inverters, and a voltage converter.  Ultimately, the failure was traced back
to a single nut and bolt in the battery bank cable connections, that had
developed hidden corrosion over time.  Corrosion causes resistance to the
flow of electricity, which in turn generates heat.  With enough corrosion,
and enough current flow, the amount of heat generated can be sufficient to
melt battery terminal connections; which is exactly what happened in xxxxx's
case.  The melted metal flowed between the negative and positive terminals
of his industrial battery, causing a high power short that was beyond the
capabilities of any of the circuit protection, resulting in the damage to
the equipment.

Now keep in mind, xxxxx is one of the more detail-oriented people we've had
here at Backwoods.  The discipline of a military background, along with
critical thinking of an engineer, were still not enough to overlook one very
tiny detail.  xxxxx does his mechanical maintenance on a routine schedule;
checking for tightness in wiring connections, cleaning accumulated spray off
battery tops, cleaning out dust and spider webs, and keeping his battery
terminal posts coated with anti-corrosion paste.  This is not the type of
person you'd expect to see such a failure.

So what happened?  It all boiled down to the battery terminal connections.
What xxxxx had NOT done, was dissembled the nut and bolts from the battery
terminals and cables to check for internal, hidden corrosion.  It had been
about 6 years since he had done that level of inspection.  When previously
reviewed, the hardware had been thoroughly inspected, cleaned, and
re-assembled, and then coated with anti-corrosion paste on the exterior.  In
one of the 16 nut/bolt pairs, a small bit of contamination or moisture must
have been left trapped inside.  Over the course of the next six years, the
corrosion grew, contaminating the entire connection; but was NOT visible
externally at all! >>

Best regards,

Dave

David Palumbo 

Independent Power LLC

462 Solar Way Drive

Hyde Park, VT 05655

802-371-8678 cell

802-888-4917 home

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170120/10a6671f/attachment-0001.html>


More information about the RE-wrenches mailing list