[RE-wrenches] AC/DC in Same Trench?

Chris Mason cometenergysystems at gmail.com
Wed Dec 28 11:58:06 PST 2016


No problem with same trench, the requirements are that they are not in the
same raceway.

On Wed, Dec 28, 2016 at 1:37 PM, Corey Shalanski <corey at joule-energy.com>
wrote:

> For some upcoming utility-scale projects our design team is wondering
> about placing direct-bury AC and DC circuits in the same trench.
> - Firstly, is this even *Code*-permissible?
> - Secondly, are there any common sense reasons (induced voltage/signal
> interference/etc) for not doing this?
>
> Thanks,
> Corey Shalanski
> Joule Energy
> New Orleans, LA
>