[RE-wrenches] Intermittent charge 4024
Drake
drake.chamberlin at redwoodalliance.org
Fri Nov 4 07:15:34 PDT 2016
I know an electronics technician who has repaired
a couple of Trace inverters for us for a very
reasonable fee. Contact me off the list for his contact info.
At 02:27 PM 11/3/2016, you wrote:
>You can replace the internal SW fans (if the fans themselves are the problem.)
>
>BUT the replacement fans must draw approximately the same current as the
>original fans because they are powered by a current source rather than voltage
>source. i.e. If you use a fan that draws less
>than the fan current, the voltage
>could rise too high. Some 12V fans don't have a problem running at say,
>20+ volts DC BTW so might not be that big of a deal.
>
>boB
>
>
>On 11/3/2016 7:57 AM, Jay wrote:
>>Hi Mac
>>
>>No don't recommend replacing internal fans
>>
>>But I have installed external 120v muffin fans on the ends.
>>Seal up the vents around the ends so it pulls air through.
>>Hook the fans to the genny input.
>>Quick and works well
>>
>>Jay
>>
>>On Nov 3, 2016, at 7:09 AM, Mac Lewis
>><<mailto:maclewis1 at gmail.com>maclewis1 at gmail.com> wrote:
>>
>>>Hello Wrenches,
>>>
>>>I recently assessed a 22 year old Trace
>>>4024. During bulk charge mode, I noticed that
>>>the charge would go from about 18A down to
>>>5-6A every 15-20 seconds, and then repeat the
>>>cycle. I observed this for about 5 minutes
>>>relatively consistently I also noticed the
>>>body of the 4024 was very hot, and I couldn't
>>>feel a fan moving air through it.
>>>
>>>I put a fan on it and blew air over the body
>>>of the inverter, trying to direct it through
>>>the machine. While I did that, I never
>>>observed it drop out again over about 5
>>>minutes, so I'm assuming that there is an
>>>internal cooling fan that has gone out.
>>>
>>>It's been quite a while since I opened one of
>>>these up. Does anyone know what's involved in
>>>replacing a cooling fan on one of these? Is
>>>it worth it on a 22 year old inverter?
>>>
>>>Thanks in advance
>>>
>>>--
>>>
>>>
>>>
>>>Mac Lewis
>>>
>>>"Yo solo sé que no sé nada." -Sócrates
>>>_______________________________________________
>>>List sponsored by Redwood Alliance
>>>
>>>List Address:
>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>
>>>Change listserver email address & settings:
>>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive:
>>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>List rules & etiquette:
>>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out or update participant bios:
>>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20161104/42f44094/attachment-0002.html>
More information about the RE-wrenches
mailing list