[RE-wrenches] Megawatt System - Combiner Output Wiring

Solar dahlsolar at gmail.com
Thu Sep 29 04:30:11 PDT 2016


The Last large system I worked on we used direct burial alum 750s. We had a large crew out that day to help with that wire pull, it was 1000'. Eventually the backhoe that dug the trench was used to help pull the wires (slowly!). I guess I'd do it that way again but I don't have lots of  experience with large systems like others might. 

Jesse Dahl

NABCEP PV Installation Professional
IBEW Local 292 - Electrician 
Electrical/Solar PV Instructor - HCC

Sent from my iPhone

> On Sep 28, 2016, at 6:32 PM, Corey Shalanski <corey at joule-energy.com> wrote:
> 
> We're in the process of designing our first >1MW system. It will include inverter output combiner panels (potential aggregate current >700A) located approx 100' from the system disconnects.
> 
> Since we have never previously dealt with wires this big (2 sets of paralleled 500 mcm?) we are thinking that direct burial (aluminum) conductors might be a good option - any suggestions? What wiring method do others use for this type of large ampacity AC circuit? UF? USE? USE-2? Other?..
> 
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160929/abb39c3b/attachment-0002.html>


More information about the RE-wrenches mailing list