[RE-wrenches] SMA Tripower
Garrison Riegel
Garrison at solarserviceinc.com
Thu Sep 1 06:38:43 PDT 2016
Hi Brian,
Can we not invoke Art. 220.5(B) Fractions of an Ampere to round down to a 30A OCPD in this case?
I suppose that .1 could be pretty significant when combining many of these inverters.
Garrison Riegel
Solar Service Inc
On Aug 31, 2016, at 11:24 PM, Brian Mehalic <brian at solarenergy.org<mailto:brian at solarenergy.org>> wrote:
Hey Wrenches-
Just a heads up on the SMA Tripower - I like the inverter, but you gotta read the install manual!
Spec sheet says 24 A continuous output current for the 20 kW Tripower. Install manual (and tech support) says 24.1. That extra .1 A takes you from a 30 A to a 35 A breaker.
Of course you should follow the install manual not the specs. But what about the label on the side of the inverter? Well I've seen more than a handful that are labeled with a flat-out 24 Aac output current. What's an installer or inspector to do besides hope mfg's can get their numbers in order?
Upon closer examination, most of the STPs are 0.1 A higher than their spec sheet per the install manual - it doesn't really make a difference on the 12 or 15 kW models - just the 20 where you have to go up 1 standard OCPD size. Pretty sure there's lots of 20 kW units out there backfeeding a 30 A breaker. Hmmmmm....
Brian Mehalic
NABCEP Certified Solar PV Installation Professional(tm) R031508-59
520.204.6639
Solar Energy International
http://www.solarenergy.org
SEI Professional Services
http://www.seisolarpros.com
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160901/0265ec66/attachment-0002.html>
More information about the RE-wrenches
mailing list