[RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?
Ray Walters
ray at solarray.com
Tue Aug 16 13:23:27 PDT 2016
My guess is that in your case the GTPV will just help alleviate the volt
drop situation. I wouldn't start adding transformers, etc until you are
having a problem. Put in the contract that this extra cost may be
necessary for proper function, but I would keep it as a backup. Based
on the numbers you just mentioned, you would only be selling a surplus
of 30 amps, and the existing wire should be adequate for that.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 8/16/2016 1:16 PM, Howard Arey wrote:
>
> Answers to all:
>
> No – I did not measure voltage at the house. Right now, only an
> assumption of voltage drop based on my perception of what “typical”
> loads might be on this 150-amp service. I wasn’t expecting to see such
> small wires for such a long run from transformer to house when I
> showed up there without a voltmeter. He is a heavy user, using 6,000
> kwh in some months
>
> We’re looking at a 20KW system (he has some other expansion
> requirements, he has the roof space, and the need.) I roughly estimate
> that he’ll use onsite 40-50 amps of the 82 amps at peak inverter power
> output.
>
> Interesting to hear of one transformer response and hope to learn more
> on that, too.
>
> *Howard “Scot” Arey*
>
> Owner, Solar CenTex
>
> 254-300-1228
>
> scot.arey at solarcentex.com
>
> www.solarcentex.com <http://www.solarcentex.com/>
>
> https://www.facebook.com/SolarCentex
>
> Rated #1 Solar Installer in Texas by Solar Reviews
> <http://www.solarreviews.com/solar-companies/top-100-residential-solar-power-contractors-2016/texas/>__
>
> Solar Centex Logo - No Back
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160816/f927ccbf/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 48536 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160816/f927ccbf/attachment-0004.png>
More information about the RE-wrenches
mailing list