[RE-wrenches] New Construction Enphase Romex / NM

Jason Szumlanski jason at floridasolardesigngroup.com
Tue Jul 26 16:38:26 PDT 2016


I installed a Soladeck on my own home early on to test it out, and I've
been very happy. I actually have the 3-circuit Enphase combiner with AC
circuit breakers. I have had a few nuisance trips, but that's more about
the breaker than the enclosure I think.

That was way back in the "early days" (haha) and I installed conduit all
the way back to the AC disconnect. Romex is leaps and bounds easier,
especially for new construction.



On Tue, Jul 26, 2016 at 5:11 PM, William Dorsett <wmdorsett at sbcglobal.net>
wrote:

> Makes sense, Jason. We always use standard metal Romex clamps. It would be
> nice if SolaDeck made a box that actually is sized for a couple branches.
> Like working on an old Ford, with these you can crawl in under the hood.
> And I remain a little skeptical that the foam gasket actually seals the
> down hill side.
>
>
>
> Bill Dorsett
>
> Manhattan, KS
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski
> *Sent:* Tuesday, July 26, 2016 2:46 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] New Construction Enphase Romex / NM
>
>
>
> August,
>
>
>
> That's exactly what we have been hit with before. I just got good news a
> few minutes ago that one major jurisdiction here made the exception to
> allow Romex into a Soladeck, and they will even consider Romex in a short
> piece of conduit to a roof mounted PVC box. In fact, the person I spoke to
> cited the outdoor electrical outlets as a prime example of where Romex is
> traditionally allowed into the back of a box in a wet location.
>
>
>
> Logic prevails!
>
>
>
> Jason
>
>
>
>
>
> On Tue, Jul 26, 2016 at 2:56 PM, August Goers <august at luminalt.com> wrote:
>
> Hi Jason,
>
>
>
> We’re in a territory where we can’t run Romex (NM) directly into Soladecks
> because of the wet location issue. I actually think inspectors are easing
> up on enforcing this particular code grey area, but nonetheless we haven’t
> run NM directly into Soladecks. I imagine that using a regular NM cable
> clamp connector would work.
>
>
>
> When we do run NM, we terminate it in indoors in a permanently accessible
> box typically located in the attic or on the ceiling or wall by the roof
> penetration location. Then, we run EMT through the roof and to our rooftop
> J-box. THWN-2 is run between these two boxes. Then, the microinverter (or
> ACPV) wire is spliced to the THWN-2 at the rooftop J-box. Yes, this means
> three wire types for each install! We’re using splice cap crimp connectors
> for all of our splices which we’re very happy with:
> http://www.idealindustries.ca/products/wire_termination/terminals_crimps/crimp_connector_splice_cap.php
> - ferrules are available for fine stranded conductors.
>
>
>
> August
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski
> *Sent:* Tuesday, July 26, 2016 9:08 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] New Construction Enphase Romex / NM
>
>
>
> It seems like most jurisdictions are now allowing a transition to Romex in
> a Soladeck box where the Romex enters the attic immediately and runs in
> protected space all the way back to a load-side interconnection or combiner
> panel. Two issues:
>
>
>
>    - How are you bringing the Romex into the back of the Soladeck?
>    Standard metallic strain relief or strain relief with rubber compression
>    gasket or other means?
>    - Assuming you can't use a Soladeck due to the roof type and are using
>    a standard PVC roof junction box mounted to a rail with conduit to get into
>    the attic, are you transitioning from Enphase cable to THWN-2 in the j-box,
>    then installing a PVC or metallic pass-through box in the attic to
>    transition to Romex? Even though it's a short distance from the j-box to
>    the point where the conduit penetrates the roof plane, it's still a wet
>    location so Romex isn't allowed. In fact, some jurisdictions are requiring
>    this even for Soladeck boxes because they consider the Soladeck an
>    enclosure in a wet location so the inside must also be considered a wet
>    location, making the transition to Romex improper in their opinion.
>
>
>
>
>
> Jason Szumlanski
>
> Florida Solar Design Group
>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160726/781da2da/attachment-0002.html>


More information about the RE-wrenches mailing list