Hilton:



I have had exactly this problem, along with several other problems, with
the Solectria inverters.  I document them all in a web page:



http://www.millersolar.com/MillerSolar/case_studies/Solectria/Solectria.html



I had a lengthy series of exchanges with Solectria and received a lot of
excuses and justifications, but no real results.  We try to avoid using
Solectria for all of these reasons and also for the fact they are no longer
an American manufacturer.



I think the most serious problem is the lack of separable DC disconnect.
This mean you have to add a 600 volt rated DC disconnect within
line-of-sight of the inverter.  This is a big expense.  Without the
disconnect, the inverter is impossible to safely service during daylight
hours.



Good luck with this install.



William







Lic 773985

millersolar.com

805-438-5600



-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Hilton Dier
Sent: Thursday, June 09, 2016 7:40 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Solectria PVI 5200 mounting



Hello Wrenches,



I have a perplexing problem with a PVI 5200 and I can't get to the front of
the tech support line at Solectria.



The inverter has the usual backplate for mounting: bolt the backplate to
the wall, lift the inverter, drop the slots on the back of the inverter
onto the tabs on top of the plate. Fine so far. Then the instructions say
to use the enclosed lock nuts to fasten the inverter to the back plate, "as
shown in figure 15."



Problem: no lock nuts, no place to put lock nuts, no indication of lock
nuts in figure 15. The inverter just hangs loose on the tabs.



I usually use SMA inverters, which have fixed nuts on the mounting frame
and matching tabs on the inverter for stainless socket head screws.



Has anyone dealt with this? I can't imagine just leaving the inverter
hanging there.



Many thanks,



Hilton



Hilton Dier III

Renewable Energy Design

Solar Gain, LLC

Missisquoi River Hydro LLC

_______________________________________________

List sponsored by Redwood Alliance



List Address: RE-wrenches at lists.re-wrenches.org



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160609/e0bc6f4b/attachment-0003.html>


More information about the RE-wrenches mailing list