Also look at the notes to the tables in Chapter 9.  For conduit fill, 
all wires are counted.  310.15 covers ampacity derating for more than 3 
current carrying conductors in the raceway. The key is "current carrying 
conductors".  The neutral definitely carries current.  You don't have to 
count grounding conductors, control, or signal wiring for that ampacity 
derating, because they don't create heat.  But they still count for 
conduit fill, though.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/21/2016 11:35 AM, Patrick A. Shortell wrote:
> You should find your answers in 310.15
>
> Patrick A. Shortell
> Licensed Master Electrician
> Certified Solar Installer
> 71 Oregon Street
> Long Beach N.Y. 11561
> Www.thesolarstorehouse.com <http://www.thesolarstorehouse.com>
>
>
> On Apr 21, 2016, at 11:56 AM, Peter Parrish 
> <peter.parrish at calsolareng.com <mailto:peter.parrish at calsolareng.com>> 
> wrote:
>
>> I am working with a customer who is doing a complete remodel and 
>> addition to his house: stripped to the open studs and floor joists, 
>> and rafters. Not a wire in the house. We have designed a 14.4 kWp PV 
>> system with 16 kW of storage for backup and load shifting. The main 
>> panel, inverters, critical load subpanel and batteries are all going 
>> to be in the garage which is about 45 feet from the house. The 
>> customer and I have identified the critical loads.
>>
>> The GC is running conduit from the main house to the garage. I have 
>> been given seven (7) 1-1/2” PVC conduits, and I am currently doing 
>> conduit fill, ampacity and voltage drop calculations for the branch 
>> circuits that represent the critical loads.
>>
>> So I have two questions:
>>
>> (1)Should I stick to a <1% voltage drop on all circuits?
>>
>> (2)Do 120 V neutrals count as current carrying conductors? I think 
>> they do, but the electrician stated quite emphatically that  they 
>> didn’t. I thought that the derating calcs for CCCs were based solely 
>> on ohmic losses and phasing was not taken into account.
>>
>> Does the NEC provide guidance on this latter situation?
>>
>> -Peter Parrish
>>
>> Peter T. Parrish, Ph.D.
>>
>> President, SolarGnosis
>>
>> 1107 Fair Oaks Ave.
>>
>> Suite 351
>>
>> South Pasadena, CA 91030
>>
>> (323) 839-6108
>>
>> petertor at pobox.com <mailto:petertor at pobox.com>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org 
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160421/686e28c5/attachment-0003.html>


More information about the RE-wrenches mailing list