[RE-wrenches] Specific AC Coupling question
drake.chamberlin at redwoodalliance.org
drake.chamberlin at redwoodalliance.org
Mon Apr 4 19:03:52 PDT 2016
Hi Allen
I haven't tried this with Schneider, but we do have one system that
frequency shifts a Fronius IG Plus 10.0 from a pair of Sunny Islands.
Maybe a different degree of shifting is present. SMA tech support felt
confident.
Drake
> Wrenches,
> Core question first: Will a ~2010 Fronius IG-4000 respond properly
> to the frequency shift regulation supplied by a new Schneider
> XW+5548 or XW+6848?
> <br>
> Situation: I haven't seen the Colorado site; I'm working as a
> consultant to produce an upgrade component list and will later serve
> as a resource during local installation of the upgrade equipment.
> Customer has hired me to turn a hodgepodge system into a GTBB
> system. The system has two key parts: an existing SW5548 with
> batteries, never properly installed (only AC1 in was ever connected
> to a main load center!) with 3.1 kW of tracker-mounted PV through an
> Outback FM60; and a roof-mounted 4kW array feeding the grid panel
> via the IG-4000. As currently installed, nothing will operate as
> wired during a grid outage, and a 240V AC well pump isn't
> supported.<br>
> <br>
> The simple plan is to replace the SW5548 with an XW+5548 or 6848
> with Midnite E-Panel; replace batteries with Surrette FLAs; keep
> existing arrays unchanged; use existing FM60 for smaller tracked
> array; use existing Fronius IG-4000 but AC couple it to the output
> of the XW. The customer understands that sell amperage is limited by
> the inverter (to 20A @ 240V for the 5548, or 4,800W, or 27A @ 240V
> for the 6848, or 6,480W) when the grid is up, but the full array can
> charge the battery bank when the grid is down.<br>
> <br>
> Schneider tech support assures me that the XW+ is good in this
> application, but I need to get an OK from Fronius about
> frequency-shift compatibility. Fronius tech support tells me that it
> may or may not work: the 0.4 hz shift is within the the normal
> frequency tolerance for this model. While the tolerance window may
> be tightened up in the field, such tightening may cause nuisance
> tripping, especially with reactive loads like a well pump or A/C.
> The tech suggested that we first test the frequency-shift approach,
> and add a DC-coil contactor between the output of the Fronius and
> the XW+ if it doesn't.
> Has anyone AC coupled these two units? Did it work? Any unexpected
> problems? Did you add a voltage-controlled contactor? What should I
> advise my client?
> Thank you,
> Allan
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list