We had that issue once. It was after a night of heavy rainfall and the
error only read for the first few early hours of the day. SMA told us it
was a poor connection in an MC4 connector that most likely got some
dampness in it...

Adam Katzman
Autonomous Energies
PO Box 1245
Kingston, NY 12402
www.autonomousenergies.com
(518) 567-1468


On Wed, Mar 23, 2016 at 5:16 PM, August Goers <august at luminalt.com> wrote:

> Hi Drake,
>
>
>
> What model SMA inverter(s) and modules do you have? We had one case where
> a MC4 connector under the array was not making good contact. It was not
> seated properly when the installer made up the connector and the arc fault
> sensor in the inverter did its job. We had another site where some
> electrical noise on the AC side, presumably a sump pump, caused the issue
> and we could not solve it so had to switch to another inverter
> manufacturer. There were other cases where the impedance or other
> electrical characteristics of the solar modules where the likely culprit.
>
>
>
> Is your roof and array totally equipment grounded?
>
>
>
> Best,
>
>
>
> August
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Drake
> *Sent:* Wednesday, March 23, 2016 2:08 PM
> *To:* RE-wrenches at lists.re-wrenches.org
> *Subject:* [RE-wrenches] AFCI trip on metal roof
>
>
>
> Hello Wrenches,
>
> We have a project with an array on a large metal roof. The AFCI has been
> tripping. Investigating the system, there is no evidence of any arcing: the
> wiring and connections are all very tight.
>
> SMA tech support says it is likely that the nuisance tripping comes from
> electrical noise getting picked up by the large metal roof.
>
> What has been your overall experience with nuisance tripping of arc fault
> protection? What were the suspected causes? What was the solution?
>
> Thanks,
>
> Drake
>
> Drake Chamberlin
>
>
>
>
>
> *Athens Electric LLCOH License 44810CO License 3773NABCEP Certified Solar
> PV 740-448-7328 <740-448-7328>*http://athens-electric.com/
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=oa-2115-v2-c>
>
> No threats detected. www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=oa-2115-v2-c>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160323/7cb2f629/attachment-0002.html>


More information about the RE-wrenches mailing list