I have often wondered this question since the Trace SW days: Since the
Radian offers generator support, why not connect the FX inverters to the
generator input of the Radian? Program the Radian to expect 30 amps per
leg. If the load exceeds 30 amps, the Radian will kick into gen-support
mode and aid the FX inverters. If the load is less than 30 amps, the
Radian goes to sleep.
William
Lic 773985
millersolar.com
805-438-5600
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Jeremy Rodriguez
Sent: Monday, February 01, 2016 7:57 PM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Increasing output Amps, Off Grid
Hello
I don't think an OB Radian can be added to an existing stacked pair of
FX's. At least easily and have all three inverters work happily with each
other. Can it?
My client is wanting more output. Even if it's just one leg of 120/240. He
is planning to wire a circuit to an outbuilding. 120 v only is fine. He
has overloaded the dual 3648 set up once before. I recommended another
pair of FX3648 inverters with autoformer.
Comments and recommendations appreciated.
Thanks in advance
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list