[RE-wrenches] large array on 200 amp service
Jason Szumlanski
jason at floridasolardesigngroup.com
Fri Sep 25 10:31:13 PDT 2015
Siemens makes a "Solar Ready" line. Whatever you plan to install, make sure
it's on the utility's list of approved devices. And...
Don't find out the hard way that your utility does not allow solar backfeed
directly to the double-lugs on the load side of the meter socket. It makes
no sense whatsoever, but we ran into one utility resisting our doing
anything in the meter can, claiming it was their domain until the
conductors leave the meter enclosure. The AHJ wasn't prepared to back us
up.
With a fusible disconnect immediately adjacent to the meter, you would
think this is the preferable interconnection method in every case from the
utility's perspective!
Jason
On Fri, Sep 25, 2015 at 11:15 AM, Peter Parrish <
peter.parrish at calsolareng.com> wrote:
> One way, if you want the feed to be on the customer’s side of the meter,
> is to install a new service panel with meter jaws that are designed to be
> “double lugged”. That is the two lugs on the customer side have
> accommodation for a solar backfeed. There are rules about the OCP and
> disconnect, but the entire arrangement is code compliant.
>
>
>
> Not every manu sells these panels, and off the top of my head I can’t
> remember the one we used many years ago. I’ll find out the make and model
> if you want.
>
>
>
> - Peter
>
>
>
> Peter T. Parrish, Ph.D.
>
> President, SolarGnosis
>
> 1107 Fair Oaks Ave.
>
> Suite 351
>
> South Pasadena, CA 91030
>
> (323) 839-6108
>
> petertor at pobox.com
>
> NABCEP Certified PV Professional #031806-26
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *gary easton
> *Sent:* Friday, September 25, 2015 6:11 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] large array on 200 amp service
>
>
>
> Hello Wrenches,
>
> What are folks doing when installing 100A plus of solar into a 200A
> service?
>
>
>
> --
>
> Gary Easton
> Appalachian Renewable Power
>
> Stewart, Ohio 45778
> NABCEP Certified Solar PV
>
> T: 740-277-8498
>
> www.arp-solar.com
>
>
> “First they ignore you. Then they laugh at you. Then they fight you. Then
> you win.”
>
> ~Ghandi
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150925/c1e22f58/attachment-0002.html>
More information about the RE-wrenches
mailing list