[RE-wrenches] Generator brains
Allan Sindelar
allan at sindelarsolar.com
Thu Jul 16 11:03:22 PDT 2015
(Accidentally hit send before finished)
A few years ago we addressed this on a Kohler 11RES installation. We put a 20w module and controller on the starting battery for the control load. The other loads - carb heater and something else I don't recall - ran off the inverter's AC, but with a manual spring-wound timer at the gennie. That way the heater load only runs when needed to prepare for a cold-weather start. Works well.
Allan, Sindelar Solar
> On Jul 16, 2015, at 8:03 AM, "frenergy" <frenergy at psln.com> wrote:
>
> Wrenches,
>
> We recently discussed the significant load the brains of many gensets requires, especially in off-grid. I have been trying to keep the start battery and brains of a Kohler 14KW gen charged with a ~40 PV. This works fine until the winter.
>
> Any issues with keeping that PV connected (with its charge controller) and re-connecting the supplied-by-Kohler power source connection to keep the battery and brains happy? I would like to think the PV would take some of the load off the AC connection to the main off-grid system, with no conflicts.
>
> TIA
>
> Bill
> Feather River Solar Electric
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list