If you are looking for Square D, Page 1-24:
http://static.schneider-electric.us/assets/digest/17601.pdf

There is a solar ready lug kit (part number SR69094A) to add lugs to the
line side of the main breaker.


The easiest combination devices I have seen have a separate standard 2-pole
breaker that is a separate service disconnect. We see these a lot, but
usually the second service disconnect is already feeding a pool subpanel or
detached garage.

Regardless of what you choose, make sure it's on the "approved list" with
your utility.


[image: Logo-Sq-80.png]

Jason Szumlanski

Principal Solar Designer

Florida Solar Design Group

(239) 491-8010 office

(239) 322-5079 direct/mobile

Authorized Sales Agent for Fafco Solar

[image: Fafco-Solar-Enphase-Logo.png]

License CVC56701

On Mon, May 25, 2015 at 12:39 AM, frenergy <frenergy at psln.com> wrote:

>  Wrenches,
>
>         Customer currently has a hacked up 200 amp Sylvania meter/mains
> panel.  He also is averaging a load of 74 KWhrs/day! which will require
> about 15  KW system size at this site.  Obviously a system this size cannot
> backfeed the busses in the load center.  Because the exiting panel is a
> mess anyway, I'm suggesting it gets changed out.
>
>         What sort of new 200 amp service would facilitate a clean supply
> side connection.  One thought is have separate Utility meter socket then a
> 12 X 12 J-box with a monster power distribution block in it and then a
> distribution panel (without the meter socket)...this being a way to insert
> a means to grid-tie between the meter and the 200 amp main breaker.  A
> little spendy but nothing like going to higher amp service to be able to
> load side connect.
>
>         A 400 amp panel is not an option as the existing 165' of 3" pvc
> underground conduit to the pole currently has 4/0 alum.  The utility says
> it would have to be 4" for the new cable and the cost $10K+ for the upgrade.
>
>         Other ideas??
>
> Thanks in advance
>
> Bill
>
> Feather River Solar Electric
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150525/fed0e2b7/attachment-0002.html>


More information about the RE-wrenches mailing list