[RE-wrenches] Discrepency between inverter kWH reading andsolar production meter
frenergy
frenergy at psln.com
Fri May 22 17:26:03 PDT 2015
Hopefully there tech department can shed some light on this for you, however, it would certainly be to SolarEdge's benefit to appear to be producing more power than it really is, well, unless, Hmmmm ..........
Bill
----- Original Message -----
From: Jarmo.Venalainen at schneider-electric.com
To: RE-wrenches
Sent: Friday, May 22, 2015 4:00 PM
Subject: Re: [RE-wrenches] Discrepency between inverter kWH reading andsolar production meter
Hi:
The difference is in the accuracy of revenue grade versus inverter KWh meters. Revenue grade is typically much more accurate.
Beyond that, even if the accuracy of both was really good at lets say +/- 0.5%, you could still get a 1% overall difference in readings as one could be +0.5% and other -0.5%, even though they are both working to spec.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Xantrex Brand | CANADA | Sales Application Engineer
Phone: +604-422-2528 | Tech Support: 800-670-0707 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.Xantrex.com | Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From: Kevin Eigel <kevin at ecohousesolar.com>
To: RE-wrenches <RE-wrenches at lists.re-wrenches.org>,
Date: 05/22/2015 02:38 PM
Subject: [RE-wrenches] Discrepency between inverter kWH reading and solar production meter
Sent by: "RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
------------------------------------------------------------------------------
I recently installed a Solaredge 7600 inverter and two feet away from it installed a GE 210 solar kWh utility grade meter. Over the course of three months the kWh production measured by the inverter is more than 200 kWh greater then the production showing on the GE meter. I changed out the GE meter for the last week and the discrepancy has continued, so it looks like it is not the meter.
I am looking for any help in understanding whey there is this large discrepancy on the kWh reading between the inverter and the production meter, when they are so close together. The Solaredge technical help desk has been of no use.
--
Kevin Eigel
President
Ecohouse Solar
1857 Northwest Blvd. Ste 201, Columbus, OH 43212
www,ecohousesolar.com
614-805-5776
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
_____________________________________________________________________________________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/9ab58fc2/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 38319 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/9ab58fc2/attachment-0025.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 4274 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/9ab58fc2/attachment-0026.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1869 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/9ab58fc2/attachment-0027.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1897 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/9ab58fc2/attachment-0028.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2041 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/9ab58fc2/attachment-0029.gif>
More information about the RE-wrenches
mailing list