[RE-wrenches] FLA battery setpoints with larger arrays

frenergy frenergy at psln.com
Fri May 22 07:28:12 PDT 2015


Hey Jay,

        From what I've heard form battery manus, the C rates likely even in a well PV-ed system still will not produce C-rates high enough to approach a high or "longevity reducing" internal battery temp, assuming a typical bulk, absorb, float cycle.  Of course, battery environmental location (typical temps) would set a baseline from which batt temp would rise from.  Here in the Sierra, ambients are not very high 95% of the time.

        Just curious, how does the wiz bang account for all loads...2 shunts?

Thanks,

Bill
Feather River Solar Electric
  ----- Original Message ----- 
  From: jay peltz 
  To: RE-wrenches 
  Sent: Thursday, May 21, 2015 8:07 PM
  Subject: Re: [RE-wrenches] FLA battery setpoints with larger arrays


  Hi Allan,


  I like the classic/wiz bang jr.  This allows really good end amp control as all loads are accounted for.


  Higher C rates equal higher internal temps which definitely will shorten the life.



  On Thu, May 21, 2015 at 10:56 AM, Allan Sindelar <allan at sindelarsolar.com> wrote:

    Wrenches,
    In the last few years I have changed my approach to off grid system sizing, primarily due to higher battery costs and lower module costs. Rather than shooting for a traditional 80-90% of winter load profile target, I will size a larger array and smaller battery bank, figuring (especially here in the sunny Southwest) that batteries will recharge more quickly, will spend more of their time full (and thus last longer), and will be at least partially charged during cloudy weather. This even allows for smaller battery banks that are cycled more deeply (as long as there's a backup gennie in the mix); the lower cost of a smaller size may allow for a set of higher-quality industrial cells.

    I first began to rethink my design approach after reading Christopher Freitas' Solar Pro article on large battery banks a few years ago. Being able to refill in a day was part of his strategic approach to battery bank design. I used and wrote about this approach in my tiny house article in the current Home Power. However, I'm just beginning to get owner feedback about greater water consumption and the need for more frequent watering. This is especially the case when I add array to an existing system, and the old watering schedule is suddenly not enough. 

    When I design new systems I now encourage larger arrays and smaller battery banks, as the batteries spend more of their time happily full and recover more quickly after a discharge period. But I am thinking that I will have to begin changing charging setpoints in response. Flooded batteries have a range of recommended bulk setpoints, from 28.8 to 29.6 volts on a 24V system. When arrays were smaller we set to the higher end of the range to take advantage of topping off when available, and a two hour or longer absorption was considered beneficial, as long as the CC could transition to float at 2% of capacity or so. With a larger array a better approach may be to lower the bulk/absorption setting, as well as reduce absorption time and raise the float transition current ("done amps"). 

    I'm writing to encourage a discussion among off grid Wrenches. Are you changing the relative relationship between array and battery capacities? If so, how are you adjusting charge controller setpoint programming? For example, how would you program a Midnite Classic, Outback FM or Schneider XW if you could achieve a C/10 or C/15 charge rate?

    Thanks, Allan

    Allan Sindelar
    allan at sindelarsolar.com
    NABCEP Certified PV Installation Professional
    NABCEP Certified Technical Sales Professional
    New Mexico EE98J Journeyman Electrician
    Founder (Retired), Positive Energy, Inc.
    505 780-2738 cell








  -- 

  Jay Peltz
  Peltz Power
  jay.peltz at gmail.com


------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: RE-wrenches at lists.re-wrenches.org

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/93316657/attachment-0002.html>


More information about the RE-wrenches mailing list