[RE-wrenches] Extreme snow load ground mount?
Glenn Burt
glenn.burt at glbcc.com
Mon Apr 27 10:19:26 PDT 2015
I have seen published an adjustment factor used when calculating pitched roof snow loads that is used to modify the published flat snow load value.
Can't put my finger on it right now, but you could probably get more information with an intern search.
I have used it on ground mount calculations.
Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.
-----Original Message-----
From: "Ray Walters" <ray at solarray.com>
Sent: 4/27/2015 12:33
To: "dana at solarwork.com" <dana at solarwork.com>; "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Extreme snow load ground mount?
Gravity only acts downward. The modules are rated to 113 PSF which is
with the module laying flat. If the module is at an angle, it can take
more downward force.
For instance if it is at 70 degree tilt, It could take a downward force
of 113 PSF / cos 70 or 330 PSF.
Its possibly reasonable to assume that the snow might not slide off, but
the total snow load is not going to act perpendicular to a tilted module.
If the AHJ wants to argue the point, ask him what the snow load
requirements are against a surface of a wall. A vertical surface would
only see wind loading, not snow loading.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/26/2015 2:32 PM, Dana wrote:
>
> Nice rack!
>
> However if the panels are not rated for more the 100-113 PSF, the
> design is still not acceptable if the AHJ wants 420 PSF right?
>
> Q – What is the stoutest PV module out there?
>
> ----------------------------------------------------------------------------
>
> Dana Orzel
>
> Great Solar Works, Inc - NABCEP # 051112-136
>
> E - dana at solarwork.com - Web - solarwork.com
>
> O - 970.626.5253 C - 208.721.7003
>
> "Responsible Technologies for Responsible People since 1988"
>
> *P*Please consider the environment before printing this email.
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *Jonathan Hill
> *Sent:* Saturday, April 25, 2015 5:33 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Extreme snow load ground mount?
>
> Lars-
>
> What Bill said. Done it several times without incident.
>
> Jonathan Hill, senior solar applications engineer
> 530-559-3781
> solarjon at gmail.com <mailto:solarjon at gmail.com>
>
> On Apr 25, 2015, at 12:48 PM, Dana <dana at solarwork.com
> <mailto:dana at solarwork.com>> wrote:
>
> What is the highest PV module snow rating? 113 PSF is the highest
> I have seen I here in CO & ID 100 is the highest required .
>
> __________________________________________________________
>
> *Dana Orzel*
>
> Great Solar Works, Inc - *NABCEP # 051112-136*
>
> dana at solarwork.com <mailto:dana at solarwork.com> -www.solarwork.com
> <http://www.solarwork.com/>
>
> *O*- 970.626.5253 *F*- 970.626.4140 c*-*208.721.7003
>
> *_"Responsible Technologies for Responsible People since 1988_**_" _*
>
> *From:*RE-wrenches
> [mailto:re-wrenches-bounces at lists.re-wrenches.org]*On Behalf
> Of*bruce at willpowerelect.com <mailto:bruce at willpowerelect.com>
> *Sent:*Saturday, April 25, 2015 1:41 PM
> *To:*RE-wrenches
> *Subject:*Re: [RE-wrenches] Extreme snow load ground mount?
>
> Would this work for you?
>
> http://willpowerelectric.blogspot.com/p/h2e-is-harsh-to-extreme-solution.html
>
> Bruce Fiero-RMI
>
> <image002.jpg>
>
> *Willpower Electric LLC*
>
> 4115 S Pacific Hwy
>
> Medford, OR 97501-9103
> *Phone:*541-535-3965
>
> *Fax:*541-512-0061
>
> *Email:*bruce at willpowerelect.com <mailto:bruce at willpowerelect.com>
>
> *Web:*www.willpower-electric.com <http://www.willpower-electric.com/>
>
> Oregon Electrical Contractor C681
>
> CCB 191852
>
> DUNS 191470363
> NABCEP Certified PV
>
> Trade Ally of Energy Trust of Oregon
> Oregon Solar Tax Credit Certified Technician
>
> *"I'd put my money on the sun and solar energy. What a source of
> power! I hope we don't have to wait until oil and coal run out
> before we tackle that." T. Edison, 1931*
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] Extreme snow load ground mount?
> From: "frenergy" <frenergy at psln.com <mailto:frenergy at psln.com>>
> Date: Fri, January 16, 2015 9:17 pm
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>>
>
>
>
> Lars,
>
> Yes, the only way you can even consider an install like
> this is a pole mount, with a steep tilt in the winter to shed
> most of the snow. It would help to know if the place will be
> used in the winter or summer and how big of an array in KW or
> Sq Ft. Customer would have to understand that you cannot
> guarantee it...there are some combinations of
> wind-snow-temp-moisture that make snow cling to anything. If
> this is permitted, start dropping off cookies to an engineer.
>
> Bill
>
> Where the Sierra meets the Cascades
>
> ----- Original Message -----
>
> *From:*Lars Ortegren <mailto:lars at cal-solar.com>
>
> *To:*RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> *Sent:*Thursday, January 15, 2015 11:30 AM
>
> *Subject:*[RE-wrenches] Extreme snow load ground mount?
>
> Wrenches,
>
> I have a fun one for you. We have a couple of potential
> clients who live in the high Sierra with a 420 LB design
> snow load. After hunting around, not even a three rail
> system comes close with any module I can find, so now I'm
> looking for a pole top that will dump the snow, and still
> handle 120 mph winds. Any ideas? I would just say sorry,
> no solar for you,but like many of you I love a challenge.
>
> --
>
> */Lars Örtegren/ President/*
>
> California Solar Electric Company
> <http://www.californiasolarco.com/>
>
> PO Box 480/149 E.Main St
> Grass Valley, CA 95945
> Phone : (530)274-3671 Fax: (530)274-7518
> */California C-10 Electrical Contractor #779624/*
>
> ATTENTION*
> *This E-mail may contain CONFIDENTIAL INFORMATION intended
> only for the use of the Individual(s) named above. If you
> are not the intended recipient of this E-mail, or the
> employee or agent responsible for delivering it to the
> intended recipient, you are hereby notified that any
> dissemination or copying this E-mail is strictly
> prohibited. If you have received this E-mail in error,
> please immediately notify us by telephone
> at_ (530)274-3671_ or E-mail l
> <http://spratt@nabcep.org/>ars at cal-solar.com
> <mailto:ars at cal-solar.com> orcontact at cal-solar.com
> <mailto:contact at cal-solar.com>.
>
> <https://www.facebook.com/CaliforniaSolarElectric>
> <http://www.yelp.com/biz/california-solar-electric-company-grass-valley>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <http://www.members.re-wrenches.org/>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[The entire original message is not included.]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150427/9a4695cf/attachment-0002.html>
More information about the RE-wrenches
mailing list