Dave dave at independentpowerllc.com
Fri Mar 27 06:55:58 PDT 2015


Tump, Allan, Bill & Jay;

 

Good advice as always. I spoke with homeowner this morning and he says that
it has been the control boards on the Frigidaire's that have failed on the
SW4048. He did get advice a couple of yrs ago to add a capacitor and that
did not help. Inverter is not having any other problems that he knows of, as
of yet. He will decide between changing the inverter or changing his washer
& dryer.

 

Thank you,

Dave 

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Tump
Sent: Friday, March 27, 2015 5:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Xantrex SW 4048 inverter and Frigidaire

 

As for the older SWs we installed the cap on the output side, that being
said I have seen GFIC outlets causing problems but I have not seen these
issues w/ my SMA SI. Sounds to me that; being the professional you are,
suggesting the replacement of the older SW with something that may be less
frustrating ( new inverters and their firm ware upgrades, less frustrating
yeah right!?) better performance and eliminating costly washer repairs. If I
were to try and rectify the issue, then I will usual start w/ the removal of
the gfic, cap on the ac output, (we would just installed it on the
questionable load's circuit,0 OR offer a credit for the old SW and try to
sell them the SMA SI 6K inverter and then work your way down to their
budget.

On Mar 27, 2015, at 12:30 AM, Allan Sindelar wrote:





Dave,
This was a Wrenches discussion topic, somewhere between 2001 and 2005.There
was a fundamental incompatibility between the SW series and the electronics
of certain new model washers. The early Maytag Neptunes and front-loading,
electronically-controlled Frigidaires had issues with the mod-sine waveform
of the SW series. I looked in my archives but have nothing saved about that.
You might find the original thread in the online archives. If the "expensive
controls" include control boards or related, this could be an ongoing issue
with this combination.

We only had one experience with the issue, and it doesn't offer a useful
solution. A Y2K installation with dual SW55548s wouldn't run a Frigidaire
front-load washer. Adding a large power capacitor across the input (per
Wrenches and possibly Xantrex tech support advice) didn't solve it;
switching the washer circuit to the other inverter did. We never did figure
that one out.

Just yesterday there was a thread here on "charging multiple battery banks"
dual systems, 24 and 48V, sharing a switched array. The 24V was a SW4024.
Many of us still care for systems based on that series, and have good
respect for it, but as they get older and support gets tougher, the energy
seems to be shifting toward replacement.
Allan

Allan Sindelar
allan at sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell



 

On 3/26/2015 8:29 PM, frenergy wrote:

Dave,

 

        Do you know what it is that's failing?...electronics or motor?  Is
it the same in both?  Have these failures been happening since the 4048 was
fired up or more recently?  Is there a lot of generator run time?

 

Bill 

 

Feather River Solar Electric

----- Original Message ----- 

From: Dave <mailto:dave at independentpowerllc.com>  

To: 'RE-wrenches' <mailto:re-wrenches at lists.re-wrenches.org>  

Sent: Thursday, March 26, 2015 5:24 PM

Subject: Re: [RE-wrenches] Xantrex SW 4048 inverter and Frigidaire

 

Wrenches,

 

Older off grid system having trouble with Frigidaire washer and dryer
needing expensive repairs every year or so when run on a Xantrex SW 4048/S
inverter manufactured in June 2005.

 

Not one of my installs so I don't know the particulars.

 

Homeowners are looking for advice on what would work better with this ten
year old SW. Or, should they invest in a new inverter? 

 

Thanks,

Dave

 

David Palumbo 

Independent Power LLC

462 Solar Way Drive

Hyde Park, VT 05655

802-888-7194

 

 


  _____  


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 
 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

 

Tump at swnl.net
<blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>
<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
www.SWNL.net

                Solarwinds Northernlights       

       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401


                              Blair "TUMP" May

               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer" 
   
              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150327/9c903dbe/attachment-0002.html>


More information about the RE-wrenches mailing list