In the 2014 NEC, 690.35(B) states that overcurrent protection for
ungrounded PV power systems must be installed in accordance with 690.9.
 690.9(E) states that an overcurrent protection device must be installed on
each ungrounded conductor, i.e. both the positive and negative in
ungrounded PV power sources.

Also note 240.15, which also requires overcurrent protection in series with
all ungrounded conductors.

Cheers,


Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org

On Sun, Mar 22, 2015 at 11:28 AM, AE Solar <autonomousenergies at gmail.com>
wrote:

> Hey Wrenchers,
> Can someone point me towards where the code references the need to
> disconnect both conductors in an install with transformerless/ungrounded
> inverters? Thanks
> Adam
>
> Adam Katzman
> Autonomous Energies
> 4872 State Route 9G
> Germantown NY, 12526
> www.autonomousenergies.com
> (518) 567-1468
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150322/2222d854/attachment-0003.html>


More information about the RE-wrenches mailing list