[RE-wrenches] Outback quad stack X240 breaker tripping

frenergy frenergy at psln.com
Mon Mar 16 07:37:58 PDT 2015


Kevin,

        Not to add any confusion but I recently had to re-program the slave in a 2 VFX with Xfrmr system as it was doing the same thing...the 2 pole xfrmr breaker was tripping when a moderate load was on.  Granted this was not happening during charging though.  I think I changed the slave from OB slave L1 to OB slave L2 and all was good.  It doesn't seem likely the programming in your case would have been messed with having been working well for years prior.  Curious to hear though of a solution eventually.

Bill

Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax
  ----- Original Message ----- 
  From: Tump 
  To: RE-wrenches 
  Sent: Monday, March 16, 2015 5:39 AM
  Subject: Re: [RE-wrenches] Outback quad stack X240 breaker tripping


  Have you turned the breaker on the t240 to the off position? One does NOT have to have that operational for the system to operate correctly.The old t240 has about the same parasitic draw as an inverter. Isolate, Isolate, Isolate. If the system functions correctly w/ the t240 off and the stacking is correct on this q stack disconnect it(the t240). Otherwise I would remove the inverter com cables and only connect 1 pair of inverters at a time, reset the mate with the correct com cables connected to P1& P2. Sometimes something so simple as disconnecting & reconnection the mate can have quite a benefit. Again I would, if you are really stuck on having the t240 operational, then try it with each inverter as a single unit then try the second set of inverters. Disconnect the #s1&2 inverters and do the same; connect #s 3&4 P1 & P2, to see exactly which component may be your problem.
  You are more then happy to contact me off list if you choose. contact info below. Tump

  On Mar 15, 2015, at 5:04 PM, Jerry Shafer wrote:


     Wrenches
    OK if the X240 blows the fuse which is on the output of the inverter while the inverter is charging, excessive current must be passing through from one inverter and back to the output of another inverter ( a form of AC coupling gone bad). The time delay fits as the inverter ramps up, I would look at the contactors in each slave as one may be hanging or ther may be a bad board, easy way to test is to isolate each inverter and with a amp meter connected at the X240 see if current goes away in the X240 as it should not be doing much with light loads on the "House" side of the inverters. The X240 is 25 amps while the inverters are 50 amps. Sounds like a interesting one to diagnose.

    Jerry



    On Wed, Mar 11, 2015 at 11:59 AM, Chris Worcester <chris at solarwindworks.com> wrote:

      Hi Kevin, 
      I have seen the  X240's  trip off like this when theyare over loaded. When this was happening to us the slave inverters had blown AC  boards and some times Control and FET boards too. We had a hard time diagnosing this as their  green lights were on.  Using a clamp on  amp meter on each inverter's AC IN conductor while charging with the gen set allowed us to compare their charging currents to each other. Typically the ones with blown  AC boards output would be close to zero amps. So the X240's were doing double duty and they will smoke too if the inverters aren't delta with. 




      Sincerely, 
      Chris Worcester
      530-448-9692 
       Sent from my Galaxy S®III



      -------- Original message --------
      From: Kevin Pegg 
      Date:03/11/2015 1:19 PM (GMT-08:00) 
      To: RE-wrenches 
      Subject: [RE-wrenches] Outback quad stack X240 breaker tripping 


      Hello Wrenches, 

      Customer in remote location has a strange situation come up on an existing system installed (by others) 6 or so years go. Quad stack VFX3648. 

      Last night gen start was triggered by low voltage - a normal system operation. 

      Approx 1h into charge, they lost 1/2 the circuits in house - L2 de-energized. Caretaker went to check power system and noticed the X240 breakers tripped. Tried to reset but it tripped out right away. So he left it as is and called me in the morning. 

      Here's what I've been able to determine today: 

      - The x240 is installed to bridge L1 & L2 on the load side. 
      - with master inverter on, 3 slaves off, both L1 and L2 energized so suggests x240 is working. 
      - within 10 seconds of generator on and charging, x240 breaker trips (and makes L2 go dark). 
      - loads are minor, ~1,000 w of misc lights and such, isn't all loaded up on one leg. 

      Appreciate any thoughts to remedy. I'm not as familiar with this config as others. 

      Kevin Pegg
      EA Energy Alternatives Ltd. 
      37471 Hwy 16 E
      Telkwa, BC  V0J 2X2
      250-846-9888
      Http://www.EnergyAlternatives.ca 



      _______________________________________________
      List sponsored by Redwood Alliance

      List Address: RE-wrenches at lists.re-wrenches.org

      Change listserver email address & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out or update participant bios:
      www.members.re-wrenches.org



      _______________________________________________
      List sponsored by Redwood Alliance

      List Address: RE-wrenches at lists.re-wrenches.org

      Change listserver email address & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out or update participant bios:
      www.members.re-wrenches.org





    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches at lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    www.members.re-wrenches.org




    Tump at swnl.net               www.SWNL.net
                    Solarwinds Northernlights       
           Serving Mid Coast Maine & Northern California
                             207-832-7574   Cl. 610-517-8401                              
                                  Blair "TUMP" May
                   ********  MAINE'S CHARTER ********
                          NABCEP    "Certified PV Installer" 
       
                  ********  MAINE'S CHARTER ********
                      Trace Xantrex "Certified" Dealer / Installer"









------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: RE-wrenches at lists.re-wrenches.org

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150316/30639efe/attachment-0002.html>


More information about the RE-wrenches mailing list