[RE-wrenches] Rapid Shut Down and the 10 Second Rule Questions
Mark Frye
markf at berkeleysolar.com
Tue Feb 3 12:10:06 PST 2015
Thanks David,
This is very helpful.
Mark Frye
On 2/3/2015 12:04 PM, David Brearley wrote:
> Mark,
>
> Bill Brooks’ rapid shutdown article for SolarPro does a nice job
> walking through the individual subsections of 690.12.
>
> He also addresses initiation device (type and location), which is not
> covered in the NEC. Here is the relevant text:
>
> *What about the rapid-shutdown initiator?*/ NEC/ 690.12 does not
> specify where you should locate the initiating device or what type of
> device you must install. This lack of detail is intended to provide
> system integrators and AHJs with the flexibility to adapt
> rapid-shutdown solutions to the complexities of the built environment.
> While the best location for a rapid-shutdown device and the required
> label is typically at or near the service equipment, the fire service
> may have preplanned emergency response tactics for some large
> commercial or industrial buildings that favor a different location.
>
> One of the simplest ways to initiate rapid shutdown is to set it up to
> occur automatically upon loss of ac power. This is why /NEC 2014 /does
> not require a specific type of rapid-shutdown initiation device. If
> you install a roof-mounted residential microinverter system or a
> commercial PV system using roof-mounted string inverters located
> within 10 feet of the array, you do not need any special equipment to
> initiate rapid shutdown; you can accomplish this function simply by
> interrupting utility-supplied power to the inverters. Some companies
> have developed various rapid-shutdown switches, and claim that rapid
> shutdown requires these extra switches. However, you have to install
> an extra rapid-shutdown switch only when you need to turn the array
> off by some means other than loss of utility power, as with
> battery-backup systems or inverters equipped with a daytime
> backup-power outlet.
>
> /NEC /690.12 does not specify how many buttons, switches or movements
> of the hand are allowed to complete rapid shutdown. Ideally, the
> process should only require one action. As written today, however, the
> language in 690.12 provides system integrators and AHJs with the
> flexibility to consider alternatives. Note that if the system design
> requires more than one action to initiate rapid shutdown, the
> 10-second time limit still applies. Therefore, where systems are
> deployed with more than one initiation device or switch, they should
> all be in close proximity so that emergency personnel can de-energize
> all of the PV system circuits on the building within 10 seconds.
> Further, labeling must clearly identify all of the initiation devices
> and all of the steps required to complete rapid shutdown.
>
> Here’s a link to the complete article: http://bit.ly/1xuDxx7
>
> I hope this is of some assistance,
>
> David Brearley
> Senior Technical Editor, /SolarPro/ magazine
> NABCEP Certified PV Installation Professional
> david.brearley at solarprofessional.com
> <mailto:david.brearley at solarprofessional.com>
> Direct: 541.261.6545
> Follow us on Twitter: @SolarPro
>
> Check out this AMAZING music video tribute to SolarPro:
> http://bit.ly/1qfMCCh
>
>
>> On Feb 3, 2015, at 1:50 PM, re-wrenches-request at lists.re-wrenches.org
>> <mailto:re-wrenches-request at lists.re-wrenches.org> wrote:
>>
>> Send RE-wrenches mailing list submissions to
>> re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>> or, via email, send a message with subject or body 'help' to
>> re-wrenches-request at lists.re-wrenches.org
>> <mailto:re-wrenches-request at lists.re-wrenches.org>
>>
>> You can reach the person managing the list at
>> re-wrenches-owner at lists.re-wrenches.org
>> <mailto:re-wrenches-owner at lists.re-wrenches.org>
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of RE-wrenches digest..."
>> When responding to posts within the Digest, be sure to restore the
>> Subject: line to the original, and please edit out any extraneous
>> lines from the quoted message.
>> Today's Topics:
>>
>> 1. Re: Rapid Shut Down and the 10 Second Rule Questions (Mark Frye)
>> 2. Re: Rapid Shut Down and the 10 Second Rule Questions
>> (Jerry Shafer)
>> 3. Re: Rapid Shut Down and the 10 Second Rule Questions (Mark Frye)
>> 4. How to isolate the array DC (Mark Frye)
>> 5. Re: How to isolate the array DC (Glenn Burt)
>> 6. Re: Rapid Shut Down and the 10 Second Rule Questions
>> (Christopher Warfel)
>> 7. Re: How to isolate the array DC (Mark Frye)
>> 8. Re: Rapid Shut Down and the 10 Second Rule Questions
>> (william at millersolar.com <mailto:william at millersolar.com>)
>> 9. Re: How to isolate the array DC (Jerry Shafer)
>> 10. Re: How to isolate the array DC (boB at midnitesolar.com
>> <mailto:boB at midnitesolar.com>)
>>
>> *From:*Mark Frye <markf at berkeleysolar.com
>> <mailto:markf at berkeleysolar.com>>
>> *To:*glenn.burt at glbcc.com <mailto:glenn.burt at glbcc.com>, RE-wrenches
>> <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>>
>> *Date:*February 2, 2015 at 3:06:39 PM CST
>> *Reply-To:*RE-wrenches <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>>
>> *Subject:**Re: [RE-wrenches] Rapid Shut Down and the 10 Second Rule
>> Questions*
>>
>>
>> I really do wonder then...
>>
>> Right now, you go up to the burning house and pull the meter, bingo,
>> no AC anywhere. So why do we need the "kill" switch next to the
>> service (or where ever).... IF you drive the roof top contactor with
>> 120vac or with 24 vdc made from a power supply powered by 120vac.
>> Either way, pull the meter, no more AC and no more power to the
>> contactor coil on the roof, so DC limited to the location of the
>> contactor.
>>
>> Not really sure how the requirement for the stop switch got into the
>> Code.
>>
>> Mark Frye
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150203/5a768a72/attachment-0002.html>
More information about the RE-wrenches
mailing list