[RE-wrenches] Magnum System - Discharged Battery Bank
All Solar, Inc.
allsolar at scswifi.net
Wed Dec 17 11:13:05 PST 2014
How about the possibility of the batteries being overcharged, thus a ruined battery bank?
I believe magnum recommends a diversion load controller with a dump load and using the frequency shift as a back up.
Jeremy Rodriguez,
President
All Solar, Inc.
1463 M
Penrose Colorado 81240
719-372-3808 office
719-372-3804 fax
www.asolarelectric.com
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> On Dec 17, 2014, at 10:36 AM, Corey Shalanski <cshalanski at joule-energy.com> wrote:
>
> Clarification and Update:
> - I believe I may have inadvertently thrown Magnum under the bus in in my initial post.
> ᐧ
> While on site yesterday I did speak with Magnum's customer support about my findings and they advised to try to trickle charge the batteries up to the minimum threshold at which the Magnum inverters would turn back on. From there we will hopefully be able to run some more determinate tests. My question about the low-battery-cutout was more intended to explore whether others have ever experienced any similar issues with this protection feature. I am finding out that the feature is only relevant during inverting (not charging) mode and so would imply that the utility feed had been cut, which does not appear to be the case.
> - Our battery distributor has lent us a 12-circuit trickle charger - one set of alligator clips per battery. I am planning to re-visit the jobsite later today to put each battery on a trickle charge, which I am told will take 1-2 weeks for any lasting change to take effect. The distributor advised to reverse the leads on the batteries with negative voltage, hoping that they may be recoverable as "reversed pole" batteries thenceforth.
>
> --
> Corey
>
>
>> On Tue, Dec 16, 2014 at 8:27 PM, <cshalanski at joule-energy.com> wrote:
>>
>> Wrenches,
>>
>> I visited a customer today whose grid-tied battery backup system suffered
>> some sort of catastrophic failure, and now I'm trying to play detective to
>> figure out what happened and whose equipment/design is to blame.
>>
>> Here is what I know so far:
>> - System is ac-coupled with a Sunny Boy 7000 (7.85kW array), Magnum
>> MS4448PAE (x2), 3 strings of 4 12v batts (705Ah total)
>> - Site visit was triggered by the Sunny Boy registering zero output via
>> online monitoring.
>> - SPST Solid state relay installed on Sunny Boy output, controlled via
>> Magnum router, serves as secondary overcharge protection to Magnum's
>> frequency shift feature. Technician who initially responded claims he
>> measured 240v across the relay's terminals - relay manufacturer claims this
>> is "100% impossible". We removed the relay from the circuit, and the Sunny
>> Boy is again operational.
>> - On arrival I found the Magnum display showing a "Low Battery Charge"
>> message with the bank measuring ~4Vdc. The individual batteries were in
>> various states of charge, ranging from high of 6.3v to low of -2.6v. These
>> measurements were taken at rest, all battery cables disconnected, and yes
>> three of the batts were registering a negative voltage.
>> - Customer reports that he was not aware of any recent prolonged power
>> outages.
>>
>> The three potential suspects would seem to be:
>> - SS relay: The customer is convinced that this is the weak link in the
>> system and somehow triggered this failure. I am not so convinced but would
>> be interested to hear recommendations for properly testing its
>> functionality.
>> - Magnum equipment: Since there is low-battery-cutout protection, why would
>> this feature not have activated and prevented the batteries from draining
>> so low?
>> - Batteries: I am not very familiar with modes of failure, but our
>> distributor suggested that an internal short could be a possibility - what
>> might have triggered this?
>>
>> Clearly I am fishing for potential leads here, so any suggestions are
>> welcome.
>>
>> Thanks!
>> --
>> Corey Shalanski
>> Joule Energy
>> New Orleans, LA
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141217/c0fce749/attachment-0002.html>
More information about the RE-wrenches
mailing list