[RE-wrenches] Magnum System - Discharged Battery Bank

Tump tump at swnl.net
Thu Dec 18 03:03:42 PST 2014


I would suggest that you totally discharge the "reversed polarity" batteries and connect them to a good charged battery they will recover their polarity and once their memory has been restored they will happily take a charge. With a completely dead battery, it is quite easy to get the battery back to taking a charge this way. Did you folks take polarity readings on each battery PRIOR to installation? I would say you have a 
 battery that shorted internally causing a total drain on the DC side.  I believe this has happened prior to this visit due to the fact that you are seeing reversed polarity batteries. The battery went totally dead then its"memory" was from the cell next to it giving a charge from the negative side of that string. Once you have a battery in that string that is reversed then it reduces the battery voltage making things really whacked. 

The relay on the SMA SB one only neds to use a SP as the inverter will shut down w/ a loss of L1 &/or L2

On Dec 17, 2014, at 12:36 PM, Corey Shalanski wrote:

> Clarification and Update:
> - I believe I may have inadvertently thrown Magnum under the bus in in my initial post. 
>> While on site yesterday I did speak with Magnum's customer support about my findings and they advised to try to trickle charge the batteries up to the minimum threshold at which the Magnum inverters would turn back on. From there we will hopefully be able to run some more determinate tests. My question about the low-battery-cutout was more intended to explore whether others have ever experienced any similar issues with this protection feature. I am finding out that the feature is only relevant during inverting (not charging) mode and so would imply that the utility feed had been cut, which does not appear to be the case.
> - Our battery distributor has lent us a 12-circuit trickle charger - one set of alligator clips per battery. I am planning to re-visit the jobsite later today to put each battery on a trickle charge, which I am told will take 1-2 weeks for any lasting change to take effect. The distributor advised to reverse the leads on the batteries with negative voltage, hoping that they may be recoverable as "reversed pole" batteries thenceforth.
> 
> --
> Corey
> 
> 
> On Tue, Dec 16, 2014 at 8:27 PM, <cshalanski at joule-energy.com> wrote:
> 
> Wrenches,
> 
> I visited a customer today whose grid-tied battery backup system suffered
> some sort of catastrophic failure, and now I'm trying to play detective to
> figure out what happened and whose equipment/design is to blame.
> 
> Here is what I know so far:
> - System is ac-coupled with a Sunny Boy 7000 (7.85kW array), Magnum
> MS4448PAE (x2), 3 strings of 4 12v batts (705Ah total)
> - Site visit was triggered by the Sunny Boy registering zero output via
> online monitoring.
> - SPST Solid state relay installed on Sunny Boy output, controlled via
> Magnum router, serves as secondary overcharge protection to Magnum's
> frequency shift feature. Technician who initially responded claims he
> measured 240v across the relay's terminals - relay manufacturer claims this
> is "100% impossible". We removed the relay from the circuit, and the Sunny
> Boy is again operational.
> - On arrival I found the Magnum display showing a "Low Battery Charge"
> message with the bank measuring ~4Vdc. The individual batteries were in
> various states of charge, ranging from high of 6.3v to low of -2.6v. These
> measurements were taken at rest, all battery cables disconnected, and yes
> three of the batts were registering a negative voltage.
> - Customer reports that he was not aware of any recent prolonged power
> outages.
> 
> The three potential suspects would seem to be:
> - SS relay: The customer is convinced that this is the weak link in the
> system and somehow triggered this failure. I am not so convinced but would
> be interested to hear recommendations for properly testing its
> functionality.
> - Magnum equipment: Since there is low-battery-cutout protection, why would
> this feature not have activated and prevented the batteries from draining
> so low?
> - Batteries: I am not very familiar with modes of failure, but our
> distributor suggested that an internal short could be a possibility - what
> might have triggered this?
> 
> Clearly I am fishing for potential leads here, so any suggestions are
> welcome.
> 
> Thanks!
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> Tump at swnl.net               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                              
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 