For anyone still following this thread:
- Contrary to the manufacturer's claim I just confirmed that it is in fact
100% possible to measure 240Vac across the contacts of this single-pole
relay *when it is switched off*. This is due to voltage sense pass-through
at the grid-tied inverter's output terminals. Many thanks to Jarmo for
helping me come to this realization - I would like to echo some of the
other Wrenches' praise of this message board, such a wonderful resource!

--
Corey Shalanski
Joule Energy
NOLA


On Wed, Dec 16, 2014 at 8:27 PM, <cshalanski at joule-energy.com> wrote:
>
>
> - SPST Solid state relay installed on Sunny Boy output, controlled via
> Magnum router, serves as secondary overcharge protection to Magnum's
> frequency shift feature. Technician who initially responded claims he
> measured 240v across the relay's terminals - relay manufacturer claims this
> is "100% impossible". We removed the relay from the circuit, and the Sunny
> Boy is again operational.
>