[RE-wrenches] Aux Output on Outback Devices
Phil Undercuffler
solarphil at gmail.com
Fri Dec 5 20:11:41 PST 2014
The AUX output is protected by a PTC, which is like an analog
auto-resetting thermal fuse. It should save you most of the time. However,
PTCs are not calibrated devices, and the trip value changes based on
resistance and impedance of the fault, temperature, lateness of day,
distance from your shop, and whether the owner is looking over your
shoulder. I don't want to depend on the PTC saving my bacon anymore than I
want to use my car's airbags. Great to know it's there, never want to make
its acquaintance.
Sorry for the news,
Phil
On Dec 5, 2014 7:10 PM, "William Miller" <william at millersolar.com> wrote:
> Jay:
>
>
>
> Is this true for an FX manufactured in 2003? What version manual is this
> from?
>
>
>
> Wm
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *jay peltz
> *Sent:* Friday, December 05, 2014 5:26 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Aux Output on Outback Devices
>
>
>
> Hi William
>
>
>
> Page 23 of the VFX manual states " will reset if short circuited, no
> fusing is required".
>
>
>
> Jay
>
> Peltz power
>
>
>
>
> On Dec 5, 2014, at 5:01 PM, "William Miller" <william at millersolar.com>
> wrote:
>
> Jay:
>
>
>
> I suspect shorting the Aux leads will kill an FX inverter. We traced the
> Aux PCB traces to the scorch marks on the control board, so it seemed
> pretty clear we had tested the scenario.
>
>
>
> William
>
>
>
>
>
> <image003.jpg>
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of *jay peltz
> *Sent:* Friday, December 05, 2014 4:25 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Aux Output on Outback Devices
>
>
>
> Hi William
>
>
>
> Supposed to be.
>
> I've tried them with too large of a relay and wouldn't work ( the relay
> that is). Dead short would be the same.
>
>
>
> But i did have a VFX 3648 many years ago that had 48v on the aux output.
> Stumped the hell out of outback. While talking to tech, they had me short
> the aux wires, and poof 1 dead inverter.
>
>
>
> Jay
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141206/2b93a445/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141206/2b93a445/attachment-0004.jpg>
More information about the RE-wrenches
mailing list