Re just completed a project for a group and they required a remote
disconnect on the roof, it is a combiner box with a contactor disconnect
that is roof mounted and 100 feet away, next to the inverters we have the
push button, I will get the brand and get it to you.
Jerry
On Mon, Oct 6, 2014 at 8:40 AM, William Miller <william at millersolar.com>
wrote:
> Wrenches:
>
>
>
> We are getting up to speed on using transformer-less inverters. I have
> advocated long for the additional safety offered by these inverters but I
> am realizing the trade-offs with the new technology: The implementation
> gets more complicated with the requirement for PV wire, OCPD and
> disconnecting means for plus and minus and plus providing Arc Flash rated
> equipment.
>
>
>
> I am currently designing a system that will locate the PV about 400 feet
> from the residence. The system will utilize 2 Solectria 5200 watt
> inverters at the residence. I would like to provide disconnecting means
> for the 4 strings at the array, in case of any needed service or
> excavating. Preferably I’d like the disconnecting means to be deployable
> by a lay person (i.e. the gardener).
>
>
>
> Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy. I
> could install an Outback 8 circuit combiner with 8 touch-safe fuse
> holders. The new combiners have had dead-fronts for a while now. The
> gardener needs only to have a Philips screw driver to open this cover. Any
> better ideas out there?
>
>
>
> Thanks,
>
>
>
> William
>
>
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141007/20f92cf3/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141007/20f92cf3/attachment-0005.jpg>
More information about the RE-wrenches
mailing list