[RE-wrenches] TL inverter with long DC Feeder
William Miller
william at millersolar.com
Tue Oct 7 08:27:58 PDT 2014
August:
I have been told I can't combine upstream of the inverter.
William
Miller Solar
> On Oct 7, 2014, at 8:03 AM, August Goers <august at luminalt.com> wrote:
>
> William,
>
> We have bumped into similar dilemmas when needing remote DC disconnects with TL inverters. I believe the Solectria you are using has two MPPTs? Ideally, you would keep each string separate to benefit from the dual trackers – this would mean four DC disconnects if you went with a standard product like a Square D HU361RB. If you combine each of the two strings out at the array(s) then you could get away with two disconnects, one for each inverter. Neither option is ideal.
>
> Best,
>
> August
>
> Luminalt
>
>