William,



We have bumped into similar dilemmas when needing remote DC disconnects
with TL inverters. I believe the Solectria you are using has two MPPTs?
Ideally, you would keep each string separate to benefit from the dual
trackers – this would mean four DC disconnects if you went with a standard
product like a Square D HU361RB. If you combine each of the two strings out
at the array(s) then you could get away with two disconnects, one for each
inverter. Neither option is ideal.



Best,



August



Luminalt



*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *William Miller
*Sent:* Monday, October 06, 2014 9:01 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder



Friends:



If only an SMA would work here. But DC volts too low. We are using
Solectria PVI5200TLS.



We do not use PV wire. We transition to THWN-2 in conduit immediately.



William


Miller Solar


On Oct 6, 2014, at 8:30 PM, Chris Mason <cometenergysystems at gmail.com>
wrote:

I presumed SMA TL series.



On Mon, Oct 6, 2014 at 10:02 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:

As i read the thread you say TL which TL SMA, AE ect. They have defferent
dc input designs

On Oct 6, 2014 12:21 PM, "jay peltz" <jay at asis.com> wrote:

I do believe the outback and midnite combiners have a lock hole to prevent
exactly your concern.

unauthorized access.



jay



peltz power

On Oct 6, 2014, at 11:40 AM, William Miller wrote:



Wrenches:



We are getting up to speed on using transformer-less inverters.  I have
advocated long for the additional safety offered by these inverters but I
am realizing the trade-offs with the new technology:  The implementation
gets more complicated with the requirement for PV wire, OCPD and
disconnecting means for plus and minus and plus providing  Arc Flash rated
equipment.



I am currently designing a system that will locate the PV about 400 feet
from the residence.  The system will utilize 2 Solectria 5200 watt
inverters at the residence.  I would like to provide disconnecting means
for the 4 strings at the array, in case of any needed service or
excavating.  Preferably I’d like the disconnecting means to be deployable
by a lay person (i.e. the gardener).



Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy.  I
could install an Outback 8 circuit combiner with 8 touch-safe fuse
holders.  The new combiners have had dead-fronts for a while now.  The
gardener needs only to have a Philips screw driver to open this cover.  Any
better ideas out there?



Thanks,



William





<image002.jpg>
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





-- 

Chris Mason

NABCEP Certified Solar PV Installer™

Solar Design Engineer

Generac Generators Industrial technician



www.cometsolar.com <http://www.cometenergysystems.com>

264.235.5670

869.662.5670

Skype: netconcepts

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141007/474dd62b/attachment-0002.html>


More information about the RE-wrenches mailing list