[RE-wrenches] Conduit supports on sloped composite shingle roofs
August Goers
august at luminalt.com
Mon Sep 22 16:49:49 PDT 2014
Hi Chris,
There are a few common methods to run conduit along the roof surface.
1. Blocks made of Trex or another similar wood substitute with
conduit fastened with 1-hole straps. Trex is typically only glued to the
roof with roofing sealant (no penetrations)
2. A more professional support such as the Chem Link KnuckleHead:
http://www.chemlink.com/index.php/chemlink-products/knuckleheads or Erico
Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf - there are
other manufacturers as well
3. Quickmount classic conduit comp mount:
http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf
For residential projects we typically use Trex. For commercial projects we
typically use the Erico Caddy. If the roof is really steep and the blocks
won’t stay put then we use the Quickmount product.
For getting through the roof we typically use a standard pipe flashing or a
SolaDeck.
Best,
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Chris Mason
*Sent:* Monday, September 22, 2014 2:43 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Conduit supports on sloped composite shingle roofs
I'm curious what methods people are using to mount, flash and stand-off
conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly
metal and concrete, so we are less that familiar with the options. We used
SnapNRack flashed mounts for the rail system, but they need a rafter under
them and the conduit run will not be above rafters.
As it is very hot here, I want to get some air between the conduit and the
roof.
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670