[RE-wrenches] wood gasification to grid

RE Ellison reellison at gmail.com
Sun Sep 21 02:08:37 PDT 2014


The inverter portion of the process at this point in time would be
relatively east to do. That's not saying that the inverter will like the
power quality. Most generators will not put out smooth enough power to allow
an inverter to connect. The engines that I have seen running on wood gas
were nowhere near smooth enough to meet an inverters interconnect standards.


After all that you get to deal with the regulatory hoops and I doubt that
would be easy.

Just some thoughts.
Bob Ellison



-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Ron Young
Sent: Saturday, September 20, 2014 8:51 PM
To: RE-wrenches
Subject: [RE-wrenches] wood gasification to grid

I have a customer who wants to use a 50kw generator converted to wood
gasification to tie into the grid. Any recommendations on the type of grid
tie gear that will be appropriate? It's a preliminary inquiry but I'm
guessing a 240v output from the generator, single phase but may be 3ph. I
see Solectria and SatCon make inverters in this range. Any suggestions
appreciated

Ron Young



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14




More information about the RE-wrenches mailing list