[RE-wrenches] Rapid shutdown questions
Mac Lewis
maclewis1 at gmail.com
Wed Aug 27 07:01:39 PDT 2014
Hi Will,
Yes I'm sure AHJ's will be all over the place for a while here in Colorado.
To clarify, is this a manual disconnect in the attic? If so, that is
really missing the whole idea of a rapid shutdown.
Thanks
On Wed, Aug 27, 2014 at 7:47 AM, Will White <William.White at rgsenergy.com>
wrote:
> Our experience in MA with rapid shutdown unfortunately varies with AHJ.
> Some are letting us put an Eaton NEMA 4 disconnect on the roof next to the
> array. Some are letting us put a disconnect in an accessible attic within
> 5’ of the penetration. Some are requiring the Midnight Birdhouse remote
> switch which is expensive.
>
>
>
> Rapid shutdown doesn’t apply to pole or ground mounts.
>
>
>
> Hope this helps.
>
>
>
> Will
>
>
>
> *Will White*
> Operations Manager - New England
>
> RGS Energy
>
> 64 Main St. |Montpelier, VT 05602
> tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
>
> *RGSEnergy.com <http://www.rgsenergy.com/> **|
> william.white at rgsenergy.com <william.white at rgsenergy.com> *
>
> *Confidentiality Note: *This e-mail message may contain confidential or
> legally privileged information and is intended only for the use of the
> intended recipient(s). Any unauthorized disclosure, dissemination,
> distribution, copying or the taking of any action in reliance on the
> information herein is prohibited. E-mails are not secure and cannot be
> guaranteed to be error free as they can be intercepted, amended, or contain
> viruses. Anyone who communicates with us by e-mail is deemed to have
> accepted these risks. RGS Energy is not responsible for errors or omissions
> in this message and denies any responsibility for any damage arising from
> the use of e-mail. Any opinion and other statement contained in this
> message and any attachment are solely those of the author and do not
> necessarily represent those of the company.
>
>
>
>
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Mac Lewis
> *Sent:* Wednesday, August 27, 2014 8:32 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Rapid shutdown questions
>
>
>
> Hello wrenches,
>
>
>
> I am still trying to wrap my head around how to comply with rapid shutdown
> in off-grid and hybrid situations. I've got a few questions that maybe you
> can help with.
>
>
>
> 1. What is a (currently listed) rapid shutdown system that will
> accommodate 8 strings? I know I can do this with Midnite combiners but as
> I understand these aren't listed yet.
>
> 2. On a remote pole mount, does rapid shutdown apply? If the intent is
> to isolate a safe zone around an array for fire fighting, it seems as
> though a standard pole mounted DC disconnect can cover this concern.
>
> 3. I estimate on a typical hybrid installation, rapid shutdown will cost
> at least $3000 to implement. This includes remote shunt trip battery
> breakers, contactors on PV side of charge controller and roof combiners,
> and running control cable from remote disconnect to all locations. As of
> now, this would also require me to modify listed interconnection equipment.
> Is this what others are finding?
>
> 4. AC coupling with microinverters may be the easiest way to comply with
> most of these requirements. However, this doesn't seem like a great
> alternative to the standard charge controller installation in an off-grid
> system.
>
>
>
> Thanks in advance for your thoughts
>
>
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140827/dd5c022d/attachment-0003.html>
More information about the RE-wrenches
mailing list