[RE-wrenches] Rapid shutdown questions

Will White William.White at rgsenergy.com
Wed Aug 27 06:47:29 PDT 2014


Our experience in MA with rapid shutdown unfortunately varies with AHJ.  Some are letting us put an Eaton NEMA 4 disconnect on the roof next to the array.  Some are letting us put a disconnect in an accessible attic within 5’ of the penetration.  Some are requiring the Midnight Birdhouse remote switch which is expensive.

Rapid shutdown doesn’t apply to pole or ground mounts.

Hope this helps.

Will

Will White
Operations Manager - New England
RGS Energy


64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980

RGSEnergy.com<http://www.rgsenergy.com/> | william.white at rgsenergy.com<mailto:william.white at rgsenergy.com>

Confidentiality Note: This e-mail message may contain confidential or legally privileged information and is intended only for the use of the intended recipient(s). Any unauthorized disclosure, dissemination, distribution, copying or the taking of any action in reliance on the information herein is prohibited. E-mails are not secure and cannot be guaranteed to be error free as they can be intercepted, amended, or contain viruses. Anyone who communicates with us by e-mail is deemed to have accepted these risks. RGS Energy is not responsible for errors or omissions in this message and denies any responsibility for any damage arising from the use of e-mail. Any opinion and other statement contained in this message and any attachment are solely those of the author and do not necessarily represent those of the company.






From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Wednesday, August 27, 2014 8:32 AM
To: RE-wrenches
Subject: [RE-wrenches] Rapid shutdown questions

Hello wrenches,

I am still trying to wrap my head around how to comply with rapid shutdown in off-grid and hybrid situations.  I've got a few questions that maybe you can help with.

1.  What is a (currently listed) rapid shutdown system that will accommodate 8 strings?  I know I can do this with Midnite combiners but as I understand these aren't listed yet.
2.  On a remote pole mount, does rapid shutdown apply?  If the intent is to isolate a safe zone around an array for fire fighting, it seems as though a standard pole mounted DC disconnect can cover this concern.
3.  I estimate on a typical hybrid installation, rapid shutdown will cost at least $3000 to implement. This includes remote shunt trip battery breakers, contactors on PV side of charge controller and roof combiners, and running control cable from remote disconnect to all locations.  As of now, this would also require me to modify listed interconnection equipment.  Is this what others are finding?
4.  AC coupling with microinverters may be the easiest way to comply with most of these requirements.  However, this doesn't seem like a great alternative to the standard charge controller installation in an off-grid system.

Thanks in advance for your thoughts


--



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates