We use a protective relay, unless using Sunny 
Islands. In this case, the relay will be 
controlled by the programmable AUX relay's12 V 
signal. Magnum does have a phase shifting 
function, but does not recommend relying on it.


At 04:40 PM 7/3/2014, you wrote:

>Wrenches
>I have not seen either a OB, Trace or Magnum do 
>a even far job of charge control or voltage 
>limiting for the batteries during AC coupling as 
>this is when the transformer is basicly going 
>backwards, it can and does but even outback says 
>you need to do a AC discounting means or AC or 
>DC load dumping. We have used OB VFX for years 
>as a AC coupled device but always have some way 
>to prevent over charge of the batteries.Â
>
>
>On Thu, Jul 3, 2014 at 12:42 PM, Drake 
><<mailto:drake.chamberlin at redwoodalliance.org>drake.chamberlin at redwoodalliance.org> 
>wrote:
>Hi Larry,
>
>In this case, the Enphase will AC couple with 
>the Magnum in the protected loads panel. The AC 
>out of the Magnum provides the micro grid to 
>which the Enphase connects. If  charging 
>exceeds loads, when the grid is down, power will 
>go to the batteries (up to the high battery 
>voltage set point). If loads are greater than 
>the output of the Enphase system, the Magnum 
>will produce power to feed the loads.
>
>Thanks,
>
>Drake
>
>
>At 10:55 AM 7/3/2014, you wrote:
>Hi Drake,
>
>If the Enphase are online, up to 60 amps (30A @ 
>240V) can be transferred through the Magnum 
>inverter to loads. The inverter is not providing 
>power to loads at that time. If the Enphase go 
>offline, the Magnum takes over using power from 
>the battery. If the load is greater than your 
>Enphase system can provide, the Magnum will 
>transfer to battery power based on the VAC 
>dropout setting. You probably want to use the 
>UPS mode (read ME-ARC manual about this).
>
>The new Magnum MSH models can combine AC input 
>power and battery power to increase the total AC 
>output capacity for starting heavy loads.
>
>Larry
>
>
>
>On Jul 3, 2014, at 7:59 AM, Drake 
><<mailto:drake.chamberlin at redwoodalliance.org>drake.chamberlin at redwoodalliance.org> 
>wrote:
>
>This information helps greatly. I really appreciate all of your expert advice.
>
>One other wild card in the installation is that 
>the inverter is going to be AC coupled with an 
>Enphase system. The Enphase system will 
>contribute greatly to the overall power 
>available in the protected loads panel. But, 
>with Magnum's slow voltage response I'm not sure 
>if the Enphase system will drop off line when 
>the pump surges, or if the Enphase power will be 
>available to help with the startup surge.
>
>Any insights on this?
>
>Thank you,
>
>Drake
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140703/68ff9c6a/attachment-0002.html>


More information about the RE-wrenches mailing list