[RE-wrenches] Combining Multiple Inverters

Nick Soleil nsoleil at enphaseenergy.com
Mon Jun 30 15:06:00 PDT 2014


Hello wrenches,

705.12(D)(1) does require a single dedicated OCPD and single disconnect for
a load side interconnection.  705.12 is only applying to the point of
connection and 705.12(D) only applies to load side connected systems less
than 100kW, otherwise 705.12(A), (B), *or *(C) applies.

The requirements of 705.12 only apply to the point of connection though.
705.21 does not seem to indicate that the disconnecting means must be
"dedicated."  In fact, 690.15 specifically states that "A single
disconnecting means in accordance with 690.17 shall be permitted for the
combined ac output of multiple inverters or ac modules.

690.15(A) in the 2014 code and 690.14(D) in the 2011 code applies to
utility-interactive inverters installed in not readily accessible
locations.  This states that a disconnecting means must be installed within
site of or in each inverter.  This disconnecting means does not need to be
suitable as service equipment [690.14(A) in 2011 and 690.13(C) in 2014.]

The disconnecting means must meet 690.17.  Article 690.17 *exception*
allows that, "

*a connector shall be allowed to be used for an ac or dc disconnecting
means, provided that it complies with 690.33..." *
In and Enphase microinverter system, the AC breaker provides for the
interruption and the ac and dc connectors provide the service disconnecting
means.  Enphase connectors meet the ac and dc connector requirements as
called out in 690.33 and are rated for the application.  690.33 calls out
that the connectors must be polarized, guarded, and of the locking type.
690.33 also allows for the disconnect to be either rated to interrupt the
current or require a tool to open the connector.

Enphase has published a couple of documents on this topic, based upon the
2011 NEC.  See attached.


On Mon, Jun 30, 2014 at 1:02 PM, Glenn Burt <glenn.burt at glbcc.com> wrote:

> What am I missing here?
>
> In the 2014 NEC, 705.21 seems to indicate that every inverter needs to
> have its own AC disconnect. Most inverters only have integrated DC
> disconnects (SMA, Power One, Fronius) as I recall. Or has this been
> interpreted to only apply to the DC side of the system?
>
>
>
> Since NYS is still on the 2008 NEC, and the handbook has a note in
> 690.64B)1:
>
> *The outputs of utility-interactive inverters may not be connected
> directly in parallel without first being connected to the required
> dedicated circuit breaker or fusible disconnecting means.*
>
>
>
> Further, I believe it can be interpreted that each inverter source circuit
> connection “shall be made at a dedicated circuit breaker or fusible
> disconnecting means” as directly quoted from 690.64(B)1.
>
>
>
> I see a dedicated OCPD being required for each inverter output, unless the
> manufacturer has installation instructions which have been approved by UL
> indicating that more than one can be paralleled and retain its listing (ala
> microinverters).
>
>
>
> -Glenn
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Corey Shalanski
> *Sent:* Monday, June 30, 2014 2:38 PM
>
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] Combining Multiple Inverters
>
>
>
> Thank you to all who responded to this thread - particularly
> Jason/Dave/Jay for pointing out the maximum OCPD requirements.
>
>
>
> Getting back to my original question.. I would like to use Dave's
> "extremely small subset" example of two SB5s operating at 277V. In this
> case, if we were to parallel the output of each inverter onto a 50A OCPD
> (#6 wire), could we downsize the wire to #10 from the split going back to
> each individual inverter? or would we be better served (required?) to run
> #6 all the way back to each unit? Since we are dealing with current-limited
> devices I would tend to think we can downsize but wanted to get Wrenches'
> feedback on this.
>
>
>
> --
>
> Corey Shalanski
>
> Joule Energy
>
> New Orleans, LA
>
>>
>
>
> On Fri, Jun 27, 2014 at 12:41 PM, <
> re-wrenches-request at lists.re-wrenches.org> wrote:
>
>
> Message: 5
> Date: Fri, 27 Jun 2014 11:32:02 -0400
> From: Dave Click <daveclick at fsec.ucf.edu>
> To: re-wrenches at lists.re-wrenches.org
> Subject: Re: [RE-wrenches] Combining Multiple Inverters
> Message-ID: <53AD8E72.4080009 at fsec.ucf.edu>
> Content-Type: text/plain; format=flowed; charset=ISO-8859-1
>
> This is an interesting conversation, but I'm not sure it's going to
> really impact anything.
>
> When an inverter is listed, it is tested with some "maximum output
> overcurrent protection" as part of its rating per UL 1741. Typically
> inverter manufacturers set this to be just above the inverter's max
> current + 25%. As you know, many inverters can work at more than one
> voltage, so for the SB5s their max current ratings at 277/240/208V are
> 18/20.8/24A, respectively. The max overcurrent protection is 50A. This
> figure often appears in the manual but not in the data sheet. For SMA,
> it's in the manuals. For some manufacturers, it's only available from
> tech support.
>
> For the Sunny Boy line, the only way you could have more than one
> inverter on a shared OCPD is if you have two SB5s operating at 277V
> (18.1A rated current each, so 2x18.1x1.25 < 50A). The SB6, SB7, and SB8
> all have currents too high to make this work, as they share the 50A max
> OCPD. The SB3/3.8/4 have a max OCPD of 30A, which is too low to
> double-up since each SB3 requires an OCPD of at least 20A. The TLs don't
> work either, as the max for any unit is too low. I don't see it in the
> SMA manual, but I know that in other manuals I've seen a manufacturer
> requirement for a dedicated OCPD. The only inverters I know of that have
> a max OCPD rating far beyond their rated current are micro-inverters.
>
> As for the shared disconnect, since at least the 2005, 690.15 has noted,
> "A single disconnecting means in accordance with 690.17 shall be
> permitted for the combined ac output of one or more inverters or ac
> modules in an interactive system." That being said, the NEC requires ac
> modules and micro-inverters to have ac disconnects (connectors,
> typically) per 690.6 and 690.15(A). 690.15 notes that an inverter be
> able to be disconnected from all sources, but if doubling up these SB5s
> you could argue that this shared disconnect accomplishes that via the
> anti-islanding protection... so I agree now that this is a grey area.
>
> Anyway, it comes down to whether it's worth worrying about this for what
> is an extremely small subset of compatible inverter configurations, when
> you can just do something like install a $50 Eaton BR24L70RP (70A bus,
> 240V, 4 spaces) with two 30A breakers and be on your way.
>
> DKC
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Cordially,

*Nick Soleil*


*Field Applications Engineer*

*Enphase Energy*

Mobile: (707) 321-2937

*The Enphase System** | *Empowering You in 2014
<http://www.enphase.com/?utm_source=emailsignature&utm_medium=release&utm_campaign=Jan14>


 1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/>

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsoleil at enphaseenergy.com


NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315

Texas Master Electrician #284451

 <nsoleil at enphaseenergy.com>

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless!”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140630/5106dcc1/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Enphase_White_Paper_AC_Connectors.pdf
Type: application/pdf
Size: 166530 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140630/5106dcc1/attachment-0010.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Enphase_White_Paper_DC_Connectors.pdf
Type: application/pdf
Size: 67522 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140630/5106dcc1/attachment-0011.pdf>


More information about the RE-wrenches mailing list