[RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

Jerry Shafer jerrysgarage01 at gmail.com
Sat Jun 21 21:30:47 PDT 2014


If you do decide to vent the battery box, The battery enclosure should be
air tight, in the event the wind is blowing higher air pressure could exist
outside and push any gases into the building. I understand that this is a
sealed battery buy they will fail and if it was me I would want then in a
sealed cabinet vented or not. I have had battery failures and its not pretty
Jerry
On Jun 21, 2014 12:30 PM, "Bob Clark" <bclark at solar-wind.us> wrote:

> RE-Wrenches:
>
> 2014 NEC 480.9 (A) has two informational notes that seem to point to the
> possibility of not having to vent AGMs.
>
> Here is what I was going to do with 8 Concorde SunXtender Batteries, 6V,
> 405Ah, L16, PVX-4050HT:
>
> 1.  Put them in a Midnite Solar, MNBE-CL16 Battery Enclosure (which is not
> a sealed box) in a “battery closet."
> 2.  Vent the box out of the top of the box and through the wall of the
> house with pipes like Kevin Pegg suggests.
>
> Do any of you see any problems with this?  Venting unnecessary?
>
> One consideration is the “next guy” who occupies this house may want
> flooded batteries, in which case, the vent system would definitely be
> necessary.
>
> Bob Clark
> bclark at solar-wind.us
>
>
>
> On Apr 4, 2014, at 2:49 PM, Kevin Pegg <kpegg at energyalternatives.ca>
> wrote:
>
>  Hi William,
>
> In the cold north here in Canada, this is the most common way we install
> batteries - within the heated envelope of a home or shop, installed in a
> sealed & vented battery enclosure.
>
> Hydrogen is easy to vent as it is lighter than air. We use a process
> similar to below. I see a lot of installations with power vents that are
> not done properly - exhaust only but no intake as example. They can also
> fail. Or installed in such a way that outside wind influences could
> actually reverse the flow and pressurize the battery box! Air flow needs to
> be balanced.
>
> http://www.bdbatteries.com/hydrogenventing.php
> To remove the thermal air currents present in a battery box venting
> system, you must create a natural heat sink between the vent tubes to
> neutralize the difference in temperature. This in turn will stagnate the
> air, allowing the hydrogen which is lighter than air, to rise and escape
> the battery box. Make sure the smaller tube, the one inside, extends to the
> bottom of the box. This will allow "heavier" fresh air to fall to the floor
> of the box and retard hydrogen entry. The intake for the hydrogen is at the
> top of the box, the exterior tube in the system. Hydrogen will travel in
> the opposite direction through the larger outer pipe as it is lighter than
> the air surrounding it. Several good methods for constructing this vent
> system exist, we particularly like to see 1/2 inch copper pipes inside 1
> inch pipe. Any highly conductive metal pipe will work it will transfer heat
> quickly. Galvanized, steel, and other pipes that spark when rubbed aren't
> as great. DO NOT USE THESE IN EARTHQUAKE ZONES.
>
> DO NOT USE PVC FOR THIS VENT SYSTEM....PVC DOES NOT CONDUCT HEAT WELL
> ENOUGH! Copper, aluminum, and other non sparking conductive metals are
> great!
> <Outlook.bmp>
>
> <Outlook.bmp>
>
> -----Original Message-----
> *From:* re-wrenches-bounces at lists.re-wrenches.org [
> mailto:re-wrenches-bounces at lists.re-wrenches.org
> <re-wrenches-bounces at lists.re-wrenches.org>]*On Behalf Of *
> william at millersolar.com
> *Sent:* April 4, 2014 9:29 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Batteries in a dwelling
>
> Friends:
>
>
>
> I am proposing installation of vented batteries in a first floor garage of
> a dwelling.  The dwelling areas are on the second floor.  I am nervous
> about the cohabitation of batteries and humans.
>
>
>
> I reviewed the NEC and could not find any prohibition.  Do any of you have
> any advice on how this is accomplished in the mot safe manor?
>
>
>
> I presume good ventilation and an otherwise sealed room are advised.  I
> will propose additional smoke detectors, locked doors and I will research
> hydrogen detectors.  A good spill kit and all PPE will be staged as usual.
>
>
>
> Thanks in advance for the forthcoming, always expert advice.
>
>
>
> William Miller
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140621/ab669a13/attachment-0002.html>


More information about the RE-wrenches mailing list