<p dir="ltr">If you do decide to vent the battery box, The battery enclosure should be air tight, in the event the wind is blowing higher air pressure could exist outside and push any gases into the building. I understand that this is a sealed battery buy they will fail and if it was me I would want then in a sealed cabinet vented or not. I have had battery failures and its not pretty<br>

Jerry</p>
<div class="gmail_quote">On Jun 21, 2014 12:30 PM, "Bob Clark" <<a href="mailto:bclark@solar-wind.us">bclark@solar-wind.us</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div style="word-wrap:break-word">RE-Wrenches:<div><br></div><div>2014 NEC 480.9 (A) has two informational notes that seem to point to the possibility of not having to vent AGMs.</div><div><br></div><div>Here is what I was going to do with 8 Concorde SunXtender Batteries, 6V, 405Ah, L16, PVX-4050HT:</div>
<div><br></div><div>1.  Put them in a Midnite Solar, MNBE-CL16 Battery Enclosure (which is not a sealed box) in a “battery closet."</div><div>2.  Vent the box out of the top of the box and through the wall of the house with pipes like Kevin Pegg suggests.</div>
<div><br></div><div>Do any of you see any problems with this?  Venting unnecessary?</div><div><br></div><div>One consideration is the “next guy” who occupies this house may want flooded batteries, in which case, the vent system would definitely be necessary.</div>
<div><br><div>
<div>Bob Clark</div><div><a href="mailto:bclark@solar-wind.us" target="_blank">bclark@solar-wind.us</a></div><div><br></div><br>

</div>
<br><div><div>On Apr 4, 2014, at 2:49 PM, Kevin Pegg <<a href="mailto:kpegg@energyalternatives.ca" target="_blank">kpegg@energyalternatives.ca</a>> wrote:</div><br><blockquote type="cite">







<div lang="EN-US" vlink="purple" link="blue">
<div><span><font face="Arial" color="#0000ff">Hi 
William, </font></span></div>
<div><span><font face="Arial" color="#0000ff"></font></span> </div>
<div><span><font face="Arial" color="#0000ff">In the 
cold north here in Canada, this is the most common way we install batteries - 
within the heated envelope of a home or shop, installed in a sealed & 
vented battery enclosure.  </font></span></div>
<div><span><font face="Arial" color="#0000ff"></font></span> </div>
<div><span><font face="Arial" color="#0000ff">Hydrogen is easy to vent as it is lighter than air. We use a process 
similar to below. I see a lot of installations with power vents that are not 
done properly - exhaust only but no intake as example. They can also fail. Or 
installed in such a way that outside wind influences could actually reverse the 
flow and pressurize the battery box! Air flow needs to be balanced. 
</font></span></div>
<div><span><font face="Arial" color="#0000ff"></font></span> </div>
<div><span><font face="Arial" color="#0000ff"><a href="http://www.bdbatteries.com/hydrogenventing.php" target="_blank">http://www.bdbatteries.com/hydrogenventing.php</a></font></span></div>
<div><span><font face="Arial" color="#0000ff">To 
remove the thermal air currents present in a battery box venting system, you 
must create a natural heat sink between the vent tubes to neutralize the 
difference in temperature. This in turn will stagnate the air, allowing the 
hydrogen which is lighter than air, to rise and escape the battery box. Make 
sure the smaller tube, the one inside, extends to the bottom of the box. This 
will allow "heavier" fresh air to fall to the floor of the box and retard 
hydrogen entry. The intake for the hydrogen is at the top of the box, the 
exterior tube in the system. Hydrogen will travel in the opposite direction 
through the larger outer pipe as it is lighter than the air surrounding it. 
Several good methods for constructing this vent system exist, we particularly 
like to see 1/2 inch copper pipes inside 1 inch pipe. Any highly conductive 
metal pipe will work it will transfer heat quickly. Galvanized, steel, and other 
pipes that spark when rubbed aren't as great. DO NOT USE THESE IN EARTHQUAKE 
ZONES. </font></span></div>
<div> </div>
<div><span><font face="Arial" color="#0000ff">DO NOT 
USE PVC FOR THIS VENT SYSTEM....PVC DOES NOT CONDUCT HEAT WELL ENOUGH! Copper, 
aluminum, and other non sparking conductive metals are great! 
<br></font></span></div>
<div><span><font face="Arial" color="#0000ff"><Outlook.bmp></font></span></div>
<div><span><font face="Arial" color="#0000ff"></font></span> </div>
<div><span><font face="Arial" color="#0000ff"><Outlook.bmp></font></span></div>
<blockquote dir="ltr" style="MARGIN-RIGHT:0px">
  <div dir="ltr" align="left"><font face="Tahoma">-----Original Message-----<br><b>From:</b> 
  <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> 
  [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]<b>On Behalf Of 
  </b><a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a><br><b>Sent:</b> April 4, 2014 9:29 
  AM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> [RE-wrenches] Batteries in a 
  dwelling<br><br></font></div>
  <div><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'">Friends:<u></u><u></u></span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'"> </span></p>
<p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'">I am proposing 
  installation of vented batteries in a first floor garage of a dwelling.  
  The dwelling areas are on the second floor.  I am nervous about the 
  cohabitation of batteries and humans.<u></u><u></u></span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'"> </span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'">I reviewed the NEC 
  and could not find any prohibition.  Do any of you have any advice on how 
  this is accomplished in the mot safe manor?  <u></u><u></u></span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'"> </span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'">I presume good 
  ventilation and an otherwise sealed room are advised.  I will propose 
  additional smoke detectors, locked doors and I will research hydrogen 
  detectors.  A good spill kit and all PPE will be staged as 
  usual.<u></u><u></u></span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'"> </span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'">Thanks in advance 
  for the forthcoming, always expert advice.<u></u><u></u></span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'"> </span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'">William 
  Miller<u></u><u></u></span></p><p class="MsoNormal"><span style="FONT-SIZE:12pt;FONT-FAMILY:'Arial','sans-serif'"> </span></p></div></blockquote></div>
_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>
Change email address & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>List rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br></blockquote></div><br></div></div><br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div>