[RE-wrenches] 2014 NEC AFCI
Kirk Herander
kirk at vtsolar.com
Wed May 28 08:57:05 PDT 2014
Hi, Why would the relay need to be on a timer?
Kirk Herander
VT Solar, LLC
Un-Common PV since 1991
www.vermontsolarnow.com
dba Vermont Solar Engineering
NABCEPTM Inaugural Certificant
VT RE Incentive Program Partner
802.863.1202
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Wednesday, May 28, 2014 11:15 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 2014 NEC AFCI
Hi Kirk
I thought about that, but you'll still need it on for the 5 minute clock.
If Nick is right and no voltage is acceptable on output side, then I don't see how even with relays etc to get it to work?
Jay
Peltz power
On May 28, 2014, at 7:32 AM, "Kirk Herander" <kirk at vtsolar.com> wrote:
Sounds like you need the load side of the AFCI to disconnect from the grid if it trips. So you could have a power relay between grid and load side of the AFCI, the relay coil energized from the line side of the AFCI, i.e. the Enphase panel the AFCI is plugged into. So if it trips, power is lost on the Enphase panel buss, and the load side relay opens, disconnecting the AFCI from the grid.
So no grid power on load side of AFCI when open. Acceptable?
Kirk Herander
VT Solar, LLC
Un-Common PV since 1991
www.vermontsolarnow.com
dba Vermont Solar Engineering
NABCEPTM Inaugural Certificant
VT RE Incentive Program Partner
802.863.1202
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Tuesday, May 27, 2014 12:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 2014 NEC
Hi Jay,
It is not acceptable to wire the AFCI breaker with the utility power on the output of the AFCI breaker. That does not meet the specifications for the AFCI breakers. These breakers are sensitive to having voltage on their output when the breaker is opened, which can damage the AFCI breakers.
Currently, there are no AFCI circuit breakers that are listed for back-feed.
On Tue, May 20, 2014 at 8:10 AM, jay peltz <jay at asis.com> wrote:
HI Will,
You can do this.
Take a standard breaker panel, install a Arc fault and run the wiring from the enphase like it is the grid: ie into the main lugs.
Then this will go out through the breaker in the correct fashion, and onto the main panel.
jay
peltz power
PS as to the code, they want it this way
On May 20, 2014, at 7:59 AM, Will White wrote:
Wrenches,
Is anyone else having problems with inspectors and the 2014 NEC? In Mass we’re having all kinds of issues with inspectors requiring/allowing an array of different things for 690.12 rapid shut down ranging from roof top disconnects, disconnects on the side of a house 20’ up, disconnects in attics, or only disconnects that can be activated on the ground. It varies between inspectors.
We’re also having problems with one inspector requiring arc fault breakers on Enphase even though there are no UL listed arc fault breakers that can be back fed or he wants us to run the trunk cable in a raceway.
It’s getting very difficult to install in Mass.
Thanks,
Will
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
<http://www.rgsenergy.com/> RGSEnergy.com | <mailto:william.white at rgsenergy.com> william.white at rgsenergy.com
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
--
Cordially,
Nick Soleil
Field Applications Engineer
Enphase Energy
Mobile: (707) 321-2937
<http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten>
<http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten> MyEnlighten is Coming. Get Ready
<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
1420 North McDowell
Petaluma, CA 94954
www.enphase.com <http://www.enphaseenergy.com/>
P: (707) 763-4784 x7267
F: (707) 763-0784
E: nsoleil at enphaseenergy.com
NABCEP Certified Solar PV Installer #03262011-300
California C10 Licensed Electrician #986315
Texas Master Electrician #284451
“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion to fission. And it just so happens that there’s an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it’s wireless!”
- William McDonough
This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140528/7a335fa3/attachment-0004.html>
More information about the RE-wrenches
mailing list