[RE-wrenches] Flashing vs Sealant... again
Ray Walters
ray at solarray.com
Wed Apr 16 15:54:21 PDT 2014
We use a stainless fender washer between the lag and L foot both to
prevent a galvanic reaction between the aluminum and zinc plating, and
to seal over the slot in the L foot. It also increases the strength to
prevent the lag from tearing through the L foot in a heavy wind load.
When we tighten it down, we always make sure that we have sealant coming
out on all sides of the L foot, and the washer. We've also used lags
with rubber sealing washers too.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/16/2014 9:52 AM, don at energysolarnow.com wrote:
> As Ray Walters wrote, L feet installed with the correct sealant have
> lasted as long as the comp roofs they're
> on.
> As can be seen in the attached pictures of L-feet on a roof that I
> will soon be repairing, the wrong sealant eventually shrinks and
> separates from the L-foot. Also the slotted hole where the lag
> penetrates is exposed. That's why flashings are used-- to cover up
> sealant that won't last.
> Thanks for all the pointers to better sealants.
>
> Don Barch
> Energy Solar
>
> Ray Walters <ray at solarray.com <mailto:ray at solarray.com>> wrote:
>
> ....If I'm putting a 2 inch hole through a roof, then that
> constitutes
> a penetration, and using a flashing is usually a good idea. But when
> I'm filling a 1/4" hole with a 5/16" lag, its really much closer to
> being a roofing attachment than a penetration.
> BTW, we're not just depending on some adhesive to stop the
> moisture. An L foot is really a 1/4" thick aluminum flashing. It has
> at least 4 sq in. of surface area held permanently in place by a
> mechanical fastener that is applying a significant amount of downward
> pressure.
> ..... L feet installed
> with the correct sealant have lasted as long as the comp roofs
> they're
> on, 30 + years.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140416/ccc0f0b4/attachment-0004.html>
More information about the RE-wrenches
mailing list