[RE-wrenches] NEC 690.10(C) talking points
Kristopher Schmid
solman at legacysolar.com
Wed Mar 19 18:19:07 PDT 2014
Dan,
690.10(C) says that you are "permitted" to supply single phase 3-wire
120/240 volt "service equipment" with 120 volts under the conditions
specified in that article. If you are installing a 240 volt inverter (or
stacking 2 120s, or using a step up transformer), 690.10(C) does not apply.
Hope that helps.
Kris
On Wed, Mar 19, 2014 at 7:40 PM, Dan Fink <danbob88 at gmail.com> wrote:
> Esteemed Wrenches;
> Can anyone here help me with some simple talking points for clients
> installing off grid systems? 240 Well pumps hard wired to panel breakers
> are common, but everybody (who has even a chance of surviving up here in
> middle of nowhere way off grid) NEEDS a 240v welder outlet in the
> garage/workshop. But 690.10(C) says no.
>
> Am I missing something obvious? What do I tell these potential clients?
>
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckville Publications LLC
> NABCEP / IREC accredited Continuing Education Providers
> 970.672.4342
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
--
Shine On!
Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installer
Licensed Wisconsin Master Electrician
BSEE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140319/605016c7/attachment-0004.html>
More information about the RE-wrenches
mailing list