[RE-wrenches] Huge battery bank recommendation
Kevin Pegg
kpegg at energyalternatives.ca
Thu Mar 13 10:31:22 PDT 2014
Hi Mac,
We fabricated and operate a similar sized (400 kWh) battery / inverter / generator hybrid system for BC Hydro, our power utility servicing a remote community. It has been online for 2 years now.
Using Dekka / East Penn D-series batteries which we had custom built to our specs.
A notable difference is we have 100 kW diesels and 60 kW inverter capacity in a 120/208 SMA inverter config (stepped up to 14.4 kV distribution). The system works really well and it currently 100% uptime for last 12 months. This is an unattended system we are onsite to maintain every 2 months. No renewable input at this time.
The sizing you have reported seems out of ratio. ~ 20 kW of charging power into a 400 kWh battery bank ie C/5. Depending on the loads the gen is carrying along with charging that could further reduce available charge capacity. That generator is going to have to run for a very long time to charge that battery. We call this the big battery blunder syndrome - which has caused many failures of such scale of system.
Kevin
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org]On Behalf Of Mac Lewis
Sent: March 11, 2014 7:27 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Huge battery bank recommendation
To clarify, this is for an off-grid application, 4 Sunny Islands, 30kW generator.
On Tue, Mar 11, 2014 at 9:16 AM, August Goers < august at luminalt.com> wrote:
Mac,
Is this for an off grid system? We're doing our first project with a Deka Unigy II battery system but they are AGM and I believe only good for grid tied battery backup or applications where you won't have a very deep depth of discharge:
http://www.dekabatteries.com/assets/base/0919c.pdf
Best,
August
August Goers
Principal
Luminalt Energy Corporation
o: 415.641.4000
m: 415.559.1525
www.luminalt.com
On Tue, Mar 11, 2014 at 6:24 AM, Mac Lewis < maclewis1 at gmail.com> wrote:
Hi wrenches,
I am consulting on a job that requires an 8000 Ahr battery bank. This is quite a bit beyond my normal battery bank realm. What would you recommend for this?
Thanks in advance
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140313/f5977e96/attachment-0004.html>
More information about the RE-wrenches
mailing list