[RE-wrenches] 690.13(A) Mistake?
Brian Mehalic
brian at solarenergy.org
Tue Mar 11 13:39:18 PDT 2014
Good catch! They made the same typo in 690.56(A) - referred to 690.31(F),
not (G) - but it was corrected on the the Sept. 16th errata. Bound to
happen when sections are getting shifted around so much. Here's a link to
the nfpa page with the (so far two) errata sheets - there's several in 690
already:
http://www.nfpa.org/codes-and-standards/document-information-pages?mode=code&code=70
My experience is shoot them an email and if warranted they'll fix it in the
next errata - contact me offline if you want my contact that has been
really helpful, but in all honesty I just sent customer service an email
and it quickly got to the right people.
Nothing like a thousands of people proof reading your work - and just like
big, new ideas, such as rapid shutdown, accuracy and clarity is just as
important to the process.
Cheers,
Brian Mehalic
NABCEP Certified Solar PV Installation Professional(tm) R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132
PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org
On Tue, Mar 11, 2014 at 3:54 PM, Nathan Charles <
ncharles at paradiseenergysolutions.com> wrote:
> Hi Wrenches,
>
> So I was reading through the handbook today and got confused on the
> exception to 690.13 which reads:
>
> 690.13(A) Exception: Installations that comply with 690.31(F) shall be
> permitted to have the disconnecting means located remote from the point of
> entry of the system conductors.
>
> That should actually be 690.31(G) correct?
>
> Best regards,
>
> --
> Nathan Charles
> Engineer
> NABCEP Certified PV Installation Professional #042013-20
> Paradise Energy Solutions
> (717) 283-2021 direct
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140311/0102533b/attachment-0004.html>
More information about the RE-wrenches
mailing list